one pipe steam
Paul S_3
Paul S_3 Member Posts: 1,291
Having problem with new installation.....piping is all correct...manufacture wants 2" header...that's what I installed...piped equalizer in 1" 1/2"....which is what manufacture states.. Dimension "A" =34".....seems like water is either backing out of boiler or not returning fast enough....on a cold start boiler lights makes steam....water in gauge glass starts to drop...it drops all the way below gauge glass....kicks on auto feeder....this all happens within five minutes...after feeder kicks on....boiler floods....also having bad water hammer in in basement radiators....like its water backing up....boiler was not skimmed yet....could the oil in water cause all of this thanks Paul S
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • wheres?
    Where's the pictures?
  • Paul S_3
    pics
    Here are some pics....I know should've used 2 risers and a bigger header but this is another companies job which I helped them install it and now problems....Paul S
    347-692-4777
    ASMHVACNYC.COM
  • Paul S_3
    more pics
    More
    347-692-4777
    ASMHVACNYC.COM
  • Paul S_3
    pic
    Pic
    347-692-4777
    ASMHVACNYC.COM
  • Bio
    Bio Member Posts: 278
    edited November 2013
    Skimming
    Seems that you need a lot of skimming and there is no port installed, look behind that insulation next to the sight glass for a plug
  • Paul S_3
    skimming
    Yes behind that insulation is a 1" 1/2" port will put full size tee to skim.....but water backing out of boiler you think is because boiler hasn't been skimmed yet? Or is the eater surging making it look like its leaving boiler.....anyway before I do anything it should be skimmed thanks Paul S
    347-692-4777
    ASMHVACNYC.COM
  • eg 50??
    Eg 50... 2" header too small?? And why wasn't it properly skimmed as needed?
  • Bio
    Skim
    Yup, oils are driving the water out of the boiler
  • Paul S_3
    Peg 50
    Peg 50=2" riser and header.....I helped another company install boiler....they do not know how to work on steam....they just wanted to go by what manufacture states...personally I never go less than 3"on any boiler....and always drop header with both risers used...I instructed them to skim boiler apparently they didn't do it and I'm back to fix problem....Paul s
    347-692-4777
    ASMHVACNYC.COM
  • according
    According to spec... riser from boiler is 2.5 inches..
  • Paul S_3
    correct me
    Correct me if im wrong but on page 17 in the installation manual it shows 2.5 inch in the white area and 2 inch in the grey shaded area....am I reading it wrong?? Thanks paul s
    347-692-4777
    ASMHVACNYC.COM
  • agreed
    I did have problem reading the new format in spec sheet... look again... one for parrallel system and other figure is for counterflow system which asked for smaller riser and header pipe.
  • Paul S_3
    skimmed
    I skimmed boiler...it helped a bit but water line is still dropping and tripping low water cut off....boiler water is clear now....thanks Paul s........also is a peg 55 which requires 3"inch riser and header should recommend to change? could that be problem
    347-692-4777
    ASMHVACNYC.COM
  • ChrisJ
    ChrisJ Member Posts: 17,074
    Manual
    I have never been able to figure out why they show two different rows of piping for the EG-40,45,50 series boilers. Personally I went with two 2" risers into a 3" header with a 2" equalizer on my EG-45. If I had to do it over again I'd use two 12" long 3" nipples into reducers for very little extra money simply because I feel it would dry the steam more.
    On an EG-55 I would rip that single 2" riser and header out as it is definitely too small and is likely causing a whole lot of water to be pulled out of the boiler with the steam.
    If it was mine, I would do two 3" risers into a 4" header but that is just my personal opinion. If its any easier you could simply add a second 2" riser but you're going to need at least a 3" header. Two 2" risers would likely work better than a single 3" one as well.
    Please be aware I am not a pro.
  • ALIGA
    ALIGA Member Posts: 194
    how much pressure is the system running at?
    Might be too much pressure, causing water to get pushed into the returns?
  • Paul S_3
    psi
    Im running boiler between 1.5psi and .5psi.....another thing if you guys look at the last pic of the takeoff to the system main ....its back pitch toward the boiler could that cause this problem...im just trying to consider all possibilities thanks Paul S
    347-692-4777
    ASMHVACNYC.COM
  • ChrisJ
    Don't know
    But the boiler isn't piped to the manufactures MINIMUM specification.
    Keep in mind that is the absolute minimum piping needed for it to function properly. Larger is better, smaller won't work.
    How much of the main is pitched back towards the boiler? If its only a few feet with no radiators in that length it shouldn't matter.
  • Paul S_3
    pitch
    The main is back pitched only about 7 feet with no radiators attached to it....paul s
    347-692-4777
    ASMHVACNYC.COM
  • ChrisJ
    7 feet
    That should be fine as there won't be much condensate at least once the pipe is warmed up.
  • Paul S_3
    3 inch
    So basically re-pipe header in 3 inch pipe with 4 inch header and all should be good?can the return be too small its 1 inch ...boiler 200,000 btu....thanks paul s
    347-692-4777
    ASMHVACNYC.COM
  • ChrisJ
    Pro
    I would prefer for a pro to comment on the return as I don't feel comfortable giving an answer. My wet return is 1 1/4" and connected to an EG-45 but there might not be any specific reason for that.
    If you're going to go with a 4" header you should do two risers from the boiler. Otherwise might be simpler to just do a single 3" riser into a 3" header. Two risers will always work better though.
  • Paul S_3
    pro's
    Any body have any insight on this.?paul s
    347-692-4777
    ASMHVACNYC.COM
  • ChrisJ
    One thing
    I can add, is my system has 1" dry returns. Two of which both feed into a single 1 1/4" wet return. This is the way it was installed in 1924.
    To me that suggests for a wet return it required more than 1" for a 150,000 btu input boiler. Other than that I really don't know.
  • Mark N
    Mark N Member Posts: 1,144
    Return
    According to LAOSH a 1" wet return can handle 700 sqft of EDR. This boiler has a single 2" riser the steam velocity is like 40 ft per second. That will pull quite a bit of water out of the boiler.
  • since
    Since u will have left over fittings when re-doing the job, so keep it 2 in for eqealizer
  • Paul S_3
    header
    Basically change the header..but why am i losing water....is that small header sucking ALL THAT WATER out of boiler to make it trip on low water?thanks PAUL S
    347-692-4777
    ASMHVACNYC.COM