one pipe steam

Paul S_3
Paul S_3 Member Posts: 1,280
Having problem with new installation.....piping is all correct...manufacture wants 2" header...that's what I installed...piped equalizer in 1" 1/2"....which is what manufacture states.. Dimension "A" =34".....seems like water is either backing out of boiler or not returning fast enough....on a cold start boiler lights makes steam....water in gauge glass starts to drop...it drops all the way below gauge glass....kicks on auto feeder....this all happens within five minutes...after feeder kicks on....boiler floods....also having bad water hammer in in basement radiators....like its water backing up....boiler was not skimmed yet....could the oil in water cause all of this thanks Paul S
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company

Comments

  • wheres?

    Where's the pictures?
  • Paul S_3
    Paul S_3 Member Posts: 1,280
    pics

    Here are some pics....I know should've used 2 risers and a bigger header but this is another companies job which I helped them install it and now problems....Paul S
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • Paul S_3
    Paul S_3 Member Posts: 1,280
    more pics

    More
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • Paul S_3
    Paul S_3 Member Posts: 1,280
    pic

    Pic
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • Bio
    Bio Member Posts: 278
    edited November 2013
    Skimming

    Seems that you need a lot of skimming and there is no port installed, look behind that insulation next to the sight glass for a plug
  • Paul S_3
    Paul S_3 Member Posts: 1,280
    skimming

    Yes behind that insulation is a 1" 1/2" port will put full size tee to skim.....but water backing out of boiler you think is because boiler hasn't been skimmed yet? Or is the eater surging making it look like its leaving boiler.....anyway before I do anything it should be skimmed thanks Paul S
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • eg 50??

    Eg 50... 2" header too small?? And why wasn't it properly skimmed as needed?
  • Bio
    Bio Member Posts: 278
    Skim

    Yup, oils are driving the water out of the boiler
  • Paul S_3
    Paul S_3 Member Posts: 1,280
    Peg 50

    Peg 50=2" riser and header.....I helped another company install boiler....they do not know how to work on steam....they just wanted to go by what manufacture states...personally I never go less than 3"on any boiler....and always drop header with both risers used...I instructed them to skim boiler apparently they didn't do it and I'm back to fix problem....Paul s
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • according

    According to spec... riser from boiler is 2.5 inches..
  • Paul S_3
    Paul S_3 Member Posts: 1,280
    correct me

    Correct me if im wrong but on page 17 in the installation manual it shows 2.5 inch in the white area and 2 inch in the grey shaded area....am I reading it wrong?? Thanks paul s
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • agreed

    I did have problem reading the new format in spec sheet... look again... one for parrallel system and other figure is for counterflow system which asked for smaller riser and header pipe.
  • Paul S_3
    Paul S_3 Member Posts: 1,280
    skimmed

    I skimmed boiler...it helped a bit but water line is still dropping and tripping low water cut off....boiler water is clear now....thanks Paul s........also is a peg 55 which requires 3"inch riser and header should recommend to change? could that be problem
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • ChrisJ
    ChrisJ Member Posts: 16,316
    edited November 2013
    Manual

    I have never been able to figure out why they show two different rows of piping for the EG-40,45,50 series boilers. Personally I went with two 2" risers into a 3" header with a 2" equalizer on my EG-45. If I had to do it over again I'd use two 12" long 3" nipples into reducers for very little extra money simply because I feel it would dry the steam more.



    On an EG-55 I would rip that single 2" riser and header out as it is definitely too small and is likely causing a whole lot of water to be pulled out of the boiler with the steam.



    If it was mine, I would do two 3" risers into a 4" header but that is just my personal opinion. If its any easier you could simply add a second 2" riser but you're going to need at least a 3" header. Two 2" risers would likely work better than a single 3" one as well.



    Please be aware I am not a pro.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • ALIGA
    ALIGA Member Posts: 194
    how much pressure is the system running at?

    Might be too much pressure, causing water to get pushed into the returns?
  • Paul S_3
    Paul S_3 Member Posts: 1,280
    psi

    Im running boiler between 1.5psi and .5psi.....another thing if you guys look at the last pic of the takeoff to the system main ....its back pitch toward the boiler could that cause this problem...im just trying to consider all possibilities thanks Paul S
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • ChrisJ
    ChrisJ Member Posts: 16,316
    Don't know

    But the boiler isn't piped to the manufactures MINIMUM specification.

    Keep in mind that is the absolute minimum piping needed for it to function properly. Larger is better, smaller won't work.



    How much of the main is pitched back towards the boiler? If its only a few feet with no radiators in that length it shouldn't matter.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Paul S_3
    Paul S_3 Member Posts: 1,280
    pitch

    The main is back pitched only about 7 feet with no radiators attached to it....paul s
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • ChrisJ
    ChrisJ Member Posts: 16,316
    7 feet

    That should be fine as there won't be much condensate at least once the pipe is warmed up.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Paul S_3
    Paul S_3 Member Posts: 1,280
    3 inch

    So basically re-pipe header in 3 inch pipe with 4 inch header and all should be good?can the return be too small its 1 inch ...boiler 200,000 btu....thanks paul s
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • ChrisJ
    ChrisJ Member Posts: 16,316
    edited November 2013
    Pro

    I would prefer for a pro to comment on the return as I don't feel comfortable giving an answer. My wet return is 1 1/4" and connected to an EG-45 but there might not be any specific reason for that.



    If you're going to go with a 4" header you should do two risers from the boiler. Otherwise might be simpler to just do a single 3" riser into a 3" header. Two risers will always work better though.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Paul S_3
    Paul S_3 Member Posts: 1,280
    pro's

    Any body have any insight on this.?paul s
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • ChrisJ
    ChrisJ Member Posts: 16,316
    One thing

    I can add, is my system has 1" dry returns. Two of which both feed into a single 1 1/4" wet return. This is the way it was installed in 1924.



    To me that suggests for a wet return it required more than 1" for a 150,000 btu input boiler. Other than that I really don't know.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Mark N
    Mark N Member Posts: 1,119
    edited November 2013
    Return

    According to LAOSH a 1" wet return can handle 700 sqft of EDR. This boiler has a single 2" riser the steam velocity is like 40 ft per second. That will pull quite a bit of water out of the boiler.
  • since

    Since u will have left over fittings when re-doing the job, so keep it 2 in for eqealizer
  • Paul S_3
    Paul S_3 Member Posts: 1,280
    header

    Basically change the header..but why am i losing water....is that small header sucking ALL THAT WATER out of boiler to make it trip on low water?thanks PAUL S
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
This discussion has been closed.