one pipe steam
Paul S_3
Member Posts: 1,280
Having problem with new installation.....piping is all correct...manufacture wants 2" header...that's what I installed...piped equalizer in 1" 1/2"....which is what manufacture states.. Dimension "A" =34".....seems like water is either backing out of boiler or not returning fast enough....on a cold start boiler lights makes steam....water in gauge glass starts to drop...it drops all the way below gauge glass....kicks on auto feeder....this all happens within five minutes...after feeder kicks on....boiler floods....also having bad water hammer in in basement radiators....like its water backing up....boiler was not skimmed yet....could the oil in water cause all of this thanks Paul S
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
0
Comments
-
wheres?
Where's the pictures?0 -
pics
Here are some pics....I know should've used 2 risers and a bigger header but this is another companies job which I helped them install it and now problems....Paul SASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
more pics
MoreASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
pic
PicASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Skimming
Seems that you need a lot of skimming and there is no port installed, look behind that insulation next to the sight glass for a plug0 -
skimming
Yes behind that insulation is a 1" 1/2" port will put full size tee to skim.....but water backing out of boiler you think is because boiler hasn't been skimmed yet? Or is the eater surging making it look like its leaving boiler.....anyway before I do anything it should be skimmed thanks Paul SASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
eg 50??
Eg 50... 2" header too small?? And why wasn't it properly skimmed as needed?0 -
Skim
Yup, oils are driving the water out of the boiler0 -
Peg 50
Peg 50=2" riser and header.....I helped another company install boiler....they do not know how to work on steam....they just wanted to go by what manufacture states...personally I never go less than 3"on any boiler....and always drop header with both risers used...I instructed them to skim boiler apparently they didn't do it and I'm back to fix problem....Paul sASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
according
According to spec... riser from boiler is 2.5 inches..0 -
correct me
Correct me if im wrong but on page 17 in the installation manual it shows 2.5 inch in the white area and 2 inch in the grey shaded area....am I reading it wrong?? Thanks paul sASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
agreed
I did have problem reading the new format in spec sheet... look again... one for parrallel system and other figure is for counterflow system which asked for smaller riser and header pipe.0 -
skimmed
I skimmed boiler...it helped a bit but water line is still dropping and tripping low water cut off....boiler water is clear now....thanks Paul s........also is a peg 55 which requires 3"inch riser and header should recommend to change? could that be problemASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Manual
I have never been able to figure out why they show two different rows of piping for the EG-40,45,50 series boilers. Personally I went with two 2" risers into a 3" header with a 2" equalizer on my EG-45. If I had to do it over again I'd use two 12" long 3" nipples into reducers for very little extra money simply because I feel it would dry the steam more.
On an EG-55 I would rip that single 2" riser and header out as it is definitely too small and is likely causing a whole lot of water to be pulled out of the boiler with the steam.
If it was mine, I would do two 3" risers into a 4" header but that is just my personal opinion. If its any easier you could simply add a second 2" riser but you're going to need at least a 3" header. Two 2" risers would likely work better than a single 3" one as well.
Please be aware I am not a pro.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
how much pressure is the system running at?
Might be too much pressure, causing water to get pushed into the returns?0 -
psi
Im running boiler between 1.5psi and .5psi.....another thing if you guys look at the last pic of the takeoff to the system main ....its back pitch toward the boiler could that cause this problem...im just trying to consider all possibilities thanks Paul SASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Don't know
But the boiler isn't piped to the manufactures MINIMUM specification.
Keep in mind that is the absolute minimum piping needed for it to function properly. Larger is better, smaller won't work.
How much of the main is pitched back towards the boiler? If its only a few feet with no radiators in that length it shouldn't matter.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
pitch
The main is back pitched only about 7 feet with no radiators attached to it....paul sASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
7 feet
That should be fine as there won't be much condensate at least once the pipe is warmed up.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
3 inch
So basically re-pipe header in 3 inch pipe with 4 inch header and all should be good?can the return be too small its 1 inch ...boiler 200,000 btu....thanks paul sASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Pro
I would prefer for a pro to comment on the return as I don't feel comfortable giving an answer. My wet return is 1 1/4" and connected to an EG-45 but there might not be any specific reason for that.
If you're going to go with a 4" header you should do two risers from the boiler. Otherwise might be simpler to just do a single 3" riser into a 3" header. Two risers will always work better though.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
pro's
Any body have any insight on this.?paul sASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
One thing
I can add, is my system has 1" dry returns. Two of which both feed into a single 1 1/4" wet return. This is the way it was installed in 1924.
To me that suggests for a wet return it required more than 1" for a 150,000 btu input boiler. Other than that I really don't know.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Return
According to LAOSH a 1" wet return can handle 700 sqft of EDR. This boiler has a single 2" riser the steam velocity is like 40 ft per second. That will pull quite a bit of water out of the boiler.0 -
since
Since u will have left over fittings when re-doing the job, so keep it 2 in for eqealizer0 -
header
Basically change the header..but why am i losing water....is that small header sucking ALL THAT WATER out of boiler to make it trip on low water?thanks PAUL SASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements