Lochinvar WHN keeps tripping Relief
Colin47
Colin47 Member Posts: 1
Hi everyone, this is my first post to this website, been reading it for a while.
My company installed a Lochinvar WHN 155 about a month ago and it seems like air is getting trapped in the system. I have gotten 2 call backs because the boiler made "a grumbling noise" and the pressure relief tripped and dumped water on the floor. I am assuming that the main boiler loop (primary loop) is getting air bound causing it to flash steam inside the boiler tripping the relief, but Im not sure because I am never there when it happens.
System info:
WHN155
primary/secondary
2 zones on secondary
1 zone is a converted gravity system
second zone is a regular copper fin baseboard loop
superstor is run off of the primary loop
extrol 60 exp tank
15PSI in gauge
There is a 1-1/4" spirovent on the supply side before the circulators, it is about 3 inches from an elbow. We have bled the system out for days and bled the radiators out, but can still hear air moving through the system. Any ideas? is the spirovent to close to an elbow?
Would extra air elimination devices help? Any input would be greatly appreciated.
  • Timco
    Timco Member Posts: 3,040
    Piping
    Any piping that would trap air?
    Does your Spiro have some flux keeping it closed?
    Did you purge? I always purge each loop / zone.
    Air trapped in boiler? After fill, try letting air out through relief or gauge?
    You must purge.
    Just a guy running some pipes.
  • kcopp
    kcopp Member Posts: 4,630
    I would pull.....
    the spirovent apart. Do you have some pix? What size are the circs? and what size in the boiler? Purging out the old gravity part will be a bit of a challenge as you cant "purge" out each rad. Gotta rely on the bleeder vents... How well did you clean the old gravity piping? There is a lot of old ferrous stuff that can gum up a system especially if a gianonni HX is involved.
  • Zman
    Zman Member Posts: 7,611
    Piping
    A picture of the boiler piping would help.Where is the exp tank?
    Carl
    Albert Einstein
    hot_rod Member Posts: 26,592
    vent on the HX
    does it have a manual, or float air vent on the header inside the boiler? Often that needs to be checked.