Secondary (MR) LWCO in Weil-McLain EG(H)?
JohnNY
JohnNY Member Posts: 3,333
NYC Code requires two LWCOs on every boiler. One operating control and manual reset. It's a challenge on the EG/H series that requires some creativity.
Where are you putting yours?
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,577
    Tight fit LWCO
    What about putting the float type on a surge column using the skim port. Pipe it so that when the LWCO is flushed, all the oils which have been flung into the column will be drained out.
    My theory is that if during boiling, maybe 5% of the surface oils will be trapped in that column every hour of boiling, and so with the weekly flush, the oil will be in the bucket.
    I wish I could draw on a photograph of mine (as Rod does so easily!) what I wish had been done, but it might reduce the need for skimming, as this could be more or less automatic.--NBC
  • JohnNY
    I tried something similar...
    a siphon tube from a high ¾" tapping, but an inspector knocked it down.
    Classes
  • JStar
    JStar Member Posts: 2,752
    LWCO
    Peerless boiler, but it's a universal application.
  • SWEI
    SWEI Member Posts: 7,348
    I think I finally got
    the automatic skim port concept.
  • JohnNY
    Hey, JStar
    I followed you down Canal Street a few days ago, trying to catch up and say hello. I lost you when you got into the Holland Tunnel.
    Thanks for the pic. My guys tried that, too, and the inspector told them the 2nd lwco had to be in the casting of the boiler.
    I can't win with this lately.
    Classes
  • JStar
    John
    When I'm driving, the rest of the world around me ceases to exist! I'm sure we'll run into each other in the future.
    Have you ever had an inspector TELL you where he wants the LWCO?
  • JohnNY
    Yes
    One inspector told us we need to install an operating LWCO in a tapping half way up the gauge glass and change the switch in the MM #67 to a manual reset switch. That worked, but it was a tight distance between LWCOs and a bouncing water line is likely to trigger the reset some day. There has to be a better way. I wish WM would add another tapping.
    Classes
  • JStar
    LWCO
    For me, I want the manual reset to be lower than the operating LWCO, for those exact nuisance calls. The equalizer will see less turbulent water, and stay cleaner than the inside of the boiler.
    You've already tried piping a tap above the water line into the unused return?
  • JohnNY
    auto on top, manual below
    Yes. One inspector is not allowing the loop of piping that holds the MRLWCO. I'm going to have to go to the Boiler Division at the NY DoB to get this straightened out. So annoying. All the inspectors have their own idea of what passes and what doesn't.
    Classes
  • ChrisJ
    ChrisJ Member Posts: 17,039
    edited October 2013
    Not a pro
    However I recall my EG-45 having spots on the rear block for tappings that weren't drilled.  What about drilling and tapping one of those for a LWCO?
    I also recall it possibly having spots for trycocks as well.  Here is a picture of the rear section on my EG-45.  I think they are identical to the front section.
    https://lh6.googleusercontent.com/-VhBsqFqaOkQ/UALuSdiR06I/AAAAAAAABCM/wz0lyMe5lBs/w1103-h827-no/boiler6.jpg