steam fitting
Paul S_3
Member Posts: 1,292
Hey everyone wanted to post my drop header installation today.....removed badly piped boiler sized new boiler to Edr of radiation....critics welcome....used both tappings.....2"....into 3"drop header with 1 1/2 equalizer....and that Dry return in back right of boiler before there was no Hartford loop....Dry return just elbowed in tee at equalizer....should I pipe a Hartford loop? Thanks Paul s
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
347-692-4777
ASMHVACNYC.COM
yes
you went his far. May as well go all the way.
http://www.massengineers.com/Documents/Hartford%20Loop.htm0 -
might as well
Yes, while ya doing the hartford loop, might as well turning that reducing el straight down to get the full benifit of the header pipe.0 -
More on that reducing elbow
in its present position, water will back up behind it, which can cause wet steam and banging. It needs to be pointed down- THEN you can elbow over to hook up to the Hartford Loop.All Steamed Up, Inc.
Consulting0 -
thanks
Thanks for your input..that equalizer will be fixed tomorrow...Paul sASM Mechanical Company
347-692-4777
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
What size
is that boiler? Looks the same as a WM EG-40 or 45?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
size
Boiler is a 100,000 btu Williamson steam boiler....I also fixed equalizer....Paul sASM Mechanical Company
347-692-4777
ASMHVACNYC.COM
is that
Better but, can't see the very top.. is that tee bullheaded??? If so.. not good.... and the main return vent, I repiped back 15 "...0 -
no
No there's no bull head tee...there's just one main Paul sASM Mechanical Company
347-692-4777
ASMHVACNYC.COM
- 116 Geothermal
- 169 Indoor-Air Quality