Laars Minitherm JVS banging/knocking
Hi,
Have 4 years old Laars Minitherm JVS boiler. recently it started to make banging/knocking sounds. It starts, works for about 15 minutes, temperature goes to about 165-170 degrees, then knocking/banging starts, I see pressure spike on pressure gauge and water spill through spirovent (it is on primary loop) occurs. Primary loop circulator was replaced by a plumber, but it did not help. Any thoughts? Thank you.
    hot_rod Member Posts: 26,592
    a flow issue
    Is it the correct size pump? Air purged out? Could be the HX is plugging up inside the tubes, it may need a chemical flush. Measure the temperature rise from supply to return.
  • theStudent
    theStudent Member Posts: 2
    Thank you
    Thank you, you were right. Yesterday we checked everything and it appears that the problem was with primary circulator loose wire. So far it works fine. Thank you very much again.
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    Thanks for the update
    It's nice to see the final result of the advice given here!--NBC