HoneyWell 8043G Zone Valve Question
Junkbox
Member Posts: 7
Can I use the 2 red wires on the zone valve ( END SWITCH) as the switch that sends 120 volts to a circulating pump?
Rated for it
End Switch Rating: 50 VA pilot duty @ 24 V; 4.4 A running with 26.4 A inrush @ 120 V
Edit: didn't think about the code issues mentioned below.0 -
relay
Use a honeywell R845A 1030 relay packageThere was an error rendering this rich post.
via a relay only
you would not want to put line voltage on the bare, exposed terminal strip connections. The space under the cover is not properly separated to mix low voltage and line voltage, if you tried to wire directly into the ZV.
A relay box is the correct and safe way to relay the voltage. Honeywell, Taco, Argo are a few common brands.Bob "hot rod" Rohr
bring it to the aquastat if you have the room
run it to the aquastat or use a relay of some sort.0
- 15.8K Strictly Steam