HoneyWell 8043G Zone Valve Question
Junkbox
Member Posts: 7
Can I use the 2 red wires on the zone valve ( END SWITCH) as the switch that sends 120 volts to a circulating pump?
0
Comments
-
Rated for it
End Switch Rating: 50 VA pilot duty @ 24 V; 4.4 A running with 26.4 A inrush @ 120 V
Edit: didn't think about the code issues mentioned below.0 -
relay
Use a honeywell R845A 1030 relay packageThere was an error rendering this rich post.
0 -
via a relay only
you would not want to put line voltage on the bare, exposed terminal strip connections. The space under the cover is not properly separated to mix low voltage and line voltage, if you tried to wire directly into the ZV.
A relay box is the correct and safe way to relay the voltage. Honeywell, Taco, Argo are a few common brands.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
bring it to the aquastat if you have the room
run it to the aquastat or use a relay of some sort.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements