BTU Meter
radmix
radmix Member Posts: 194
I'm looking for a affordable BTU meter to separate 5 zones of hydronic heat in an apartment building that fed by one boiler.
    Jamie Hall Member Posts: 26,766
    You might find one
    but I'll bet it would be a little pricey.  Wouldn't it be simpler to put a run time meter -- they're absurdly cheap -- on each pump or zone valve, to record the time when the zone was calling?  It might not be quite as accurate (and I suppose if one of your tenants is a lawyer they might get torqued) but it certainly should do the job.
  • Runtime meter
    Not only are they absurdly cheap, but also surprisingly accurate. You are going to be able to calculate the percentage of total fuel use required for a single zone. If zone one has used 10 hours of pumping, zone 2 also 10 hours, and zone 3 15 hours, then 1, and 2 will have used 2/7 each, and zone 3, 3/7 of the total cost of fuel used. It could be seen from this example that zone 3 was cold-blooded, and had set the thermostat higher than the others.
    The drawback to this system is the need to read the meters on the same day as the main meter is read.
    If a lawyer can argue against this method, it would only be as a result of proving that the system has been badly maintained, and therefore has inequalities in the hot water distribution.--NBC
  • radmix
    run time meter
    Any suggestions on a brand of run time meter that I should be looking at?
  • Steve Whitbeck
    Steve Whitbeck Member Posts: 669
    Hour meter
    The problem with using an hour meter is it only shows the time that a thermostat is on. It doesn't show IF the zone valve is open or IF the boiler is running. Also it doesn't measure water flow. so if one zone is 3/4 inch and runs 10 hours it will flow a lot more BTU's than 10 hours of a 1/2 inch zone. Also if one loop is longer than the other it will flow less.
  • archibald tuttle
    archibald tuttle Member Posts: 1,154
    edited December 2013
    just ran into precisely this problem today . . .
    hour meters on zones that have radically different amounts of radiation don't tell you anything about relative consumption of fuel being divided up, unless a highly educated correction is made based on radiation per zone is made. And tell the tenant who is going to have to pay more than their proportion of hours suggest because they have more radiation and they will suddenly become ignorant of heat transfer science --  if they ever knew anything about it.
    And even then, you can still have significant discrepencies if flow rate varies given head pressure including piping and gravity resistance, air in loops, etc.
    supposedly iWorx from TACO does this but i don't know where that is really going.  don't see components for sale anywhere.  maybe they are so specialized you don't find them on the net the way you do TACO's other offerings, but I notice one iWorx component that was listed on pexsupply.com has been discontinued.
    found some non-TACO btu meters that appear to be in the $750 to $1000 range. That is a little pricey, i could maybe see under $500.  And there is the problem, as others have pointed out, that when some tenant wants to lawyer up, the sods down at your local public utilities regulators frown on these arrangements.  which is stupid of course, because, even if they are imperfect or meters are not utility grade, without an ability to make an approximation of splitting the utility bill, inhabitants have no incentive to conserve as the only alternative is to charge as a percentage of the building area regardless of whether they set their thermostats low or high.
    With the advent of smaller modulating boilers this problem may evenutally go away as this hour meter type energy split is common in many condo conversions from the 80s when there weren't boilers available with low enough firing rate to not be overfired for individual apartments.  Of course the expense of boiler replacements is more than anyone has in mind when they go to get the metering as fair as possible, but before i'd spend in the thousands on a meter for each apartment i'd consider putting the money toward separate boilers.
    That said, if anyone has had good experience with a btu meter and estimates that one can be bought and installed more like $500
  • Weezbo
    Weezbo Member Posts: 6,231
    lets consider an oblong box
    it has an apartment at each end and 3 in the middle .
    the two end apartments have three walls to the exterior or "To the Weather"
    the other three see the inside walls of the adjacent apartments ...
    no doubt this inspired Edward Allen Poe to write this story ...
  • archibald tuttle
    the boiler of Amontillado?
    if i don't laugh about this, i'll cry, so thanks
  • archibald tuttle
    nice
    that badger is the meter i was looking at as an alternative but this is $200 cheaper than i was finding.
    brian
  • Rich_49
    Rich_49 Member Posts: 2,785
    This is
    the perfect place for Delta T pumping as part of the arrangement .   All you need is to know the GPM . No lawyer can argue against  A proven equation
       Apt #1      225 Gallons =  2,250,000 BTU  /  10000    or   the dreaded 22.5  THERMS  . No argument can be made at that point .  Run time can present a problem .  This type of system can be hooked right up to a BMS so the utility can generate the bills for each tenant to avoid further hassle .  How do they currently produce DHW ?
    732-751-1560
    Rich McGrath 732-581-3833
  • Weezbo
    There can be other minor technicalities ,
    i know many of them i just do not want to elucidate upon them at the moment.
    There are things in the world,
    at Play,
    that revel in absurdity and will likely continue long after we are dead and gone .
    let us just say things may not always appear as simple as we thought.
    May tomorrow be a better day .
  • Paul Pollets
    Paul Pollets Member Posts: 3,671
    BTU metering
    Ista makes a quality meter. I've used their systems several times. There is no such thing as
    an inexpensive meter. The savings of using one boiler rather than 5 more than covers the costs. Pay the Piper or divide by 5.
    http://www.ista.com/en/products/heat_meter/
  • Metering the heat
    If all the zones, and loops are at the same temperature, then meters for the total flow (like water meters) would enable you to charge fairly.
    If you add all the meter readings up every month, and then find the percentage of the total flow for each unit from it's meter, that seems fair to me.
    Have you been charging for the heating up to now?
    If you see the open windows of wasteful apartments, then outdoor reset could discourage that by lowering the water temperature in relation to the out door temperature.
    Alternatively, you could apportion the cost on a square foot basis. --NBC
  • SWEI
    SWEI Member Posts: 7,348
    Measuring flow
    will work as long as every metered branch has the same ∆T.  I'm skeptical that would actually happen, even with ∆T pumps all around.
  • Paul48
    Paul48 Member Posts: 4,469
    headache
    For every measure to make it fair, there are counter points. Can you charge more in an apartment, because you don't have enough radiation for the heat loss? I don't know the answer, but the question is, headache producing. Do the folks on the north side of the building have to pay more? Try and convince a person  that it was fair for them to pay more for their unit, even though its the same size as another unit.
  • SWEI
    Individual BTU meters
    are the only way to do this fairly IMO.  Just like electrical submeters we see in commercial buildings, it becomes part of the lease terms.
  • Bob Vennerbeck
    Bob Vennerbeck Member Posts: 107
    affordable run-time meters
    I completely understand why simple run-time meters are not going to be as accurate as actual BTU meters - but for those of us just watching our own systems, or not renting to lawyers....
    http://www.alliedelec.com/search/productdetail.aspx?SKU=70115426
    particularly nice because you can hang it on almost any circuit - low or high voltage, AC or DC, and it's cheap enough to use as many as you'd like...
    Vbob
  • BarryNY
    BarryNY Member Posts: 13
    where does this get connected
    Hi - I have a Riello burner working a Buderus.
    Want to watch my runtime and was shocked to see that a runtime meter is not included with the Fuel Smart Hydrostat 3250 plus control unit.
    If this is a simple solution - where does it get wired into the system?
    Thanks.
