radiator for baseboard
wetheat
Hello, we are considering removing a radiator and replacing it with cast iron baseboard. How do I determine the BTUs of the radiator? Its an old radiator, and its stamped rococo. 38" high and it has 6 sections with a total length of around 18". Its a hot water system. I can size the new baseboard but need help with the output of the radiator. Thanks!
Btu/hr Of the Radiator
Is irrelevant. Need to calculate a heat loss for the room and size the baseboard to the heat loss.There was an error rendering this rich post.
hmmmm
I don't think it is irrelevant if the radiator was sized correctly, and it was.
These math security questions to post are tough!!!0 -
That Magic Word
"If"...How do you know that it was? Also a radiator capable btu/hr out put with 180 degree water is 170 btu/hr per sqft of edr, fin tube baseboard output based on a 1gpm flow rate is 560 btu/hr sqft.
May I suggest http://www.slantfin.com/index.php/homeowners-page/ipadapp for a heat loss application.
You also don't want to mix different types of radiation on the same zone.There was an error rendering this rich post.
Then
I think it is right because my father sized the radiator (and the whole house) and he knew what he was doing. I did run a load calc on the room, but I want to size it correctly based on empirical evidence. The house, as it is now, heats perfectly and is in very good balance. I know that it works great so I want to know how much heat the radiator is putting out and compare it to the load calc that I did.
I don't believe in too much information to make a decision. I want to know what I am replacing. If you can help me there, I'd appreciate it. Thanks.0 -
I think
That radiator was made by The American Radiator Company. I have the information at home. Ill post it tonight.
Just curious, if it is sized correctly why are you replacing it? leaking? Interior decoration change?0 -
correct
Thanks Robert, you are correct it was made by American Radiator. Thanks for looking into it for me.
We are changing it because of room design. I know we are not supposed to use different types of radiation on the same zone, but I am not too worried about it with cast iron radiators and one piece of cast iron baseboard. I'll probably put a Danfoss valve on one of them to fine tune the control in that room.0 -
Rococo
If is 6 sections and 18" long, that should be a four column Rad. (verify please)
If so, 6 section, 4 Col, 38" = 48 sqft. or EDR.
there are a few resources around to get the BTUH knowing the EDR and water temp.
there is a nice chart on page two of this pdf:
http://www.columbiaheating.com/page_images/Sizing%20Cast%20Iron%20Radiator%20Heating%20Capacity%20Guide.pdf0 -
correct
Robert, you are correct it is 4 column. Thanks for your help.0
- 87.8K THE MAIN WALL
- 133 Chimneys & Flues
- 79 Pipe Deterioration