                    Schlitz                
                
                    Member Posts: 1                
            
                        
            
                    I'm installing central AC, into my forced hot air system.  I need to install a R8184M control in place of the R7184B control need some wiring help. Have new T-stat and wires installed, from T-stat to the new R8184M controller.  Do I just jump the red and white wires from the new control to the old Red/white connections?
                  
                0                
            Comments
- 
            Don't do it
 there is an A/C adapter for the R7184 series that includes the transformer and extra terminals you need.
 If you use the R8184M, you'll lose the valve-on delay feature that the manufacturer specified. That can cause operational problems and warranty issues.All Steamed Up, Inc.
 Towson, MD, USA
 Steam, Vapor & Hot-Water Heating Specialists
 Oil & Gas Burner Service
 Consulting0