New control help
Schlitz
Member Posts: 1
I'm installing central AC, into my forced hot air system. I need to install a R8184M control in place of the R7184B control need some wiring help. Have new T-stat and wires installed, from T-stat to the new R8184M controller. Do I just jump the red and white wires from the new control to the old Red/white connections?
0
Comments
-
Don't do it
there is an A/C adapter for the R7184 series that includes the transformer and extra terminals you need.
If you use the R8184M, you'll lose the valve-on delay feature that the manufacturer specified. That can cause operational problems and warranty issues.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0