diverter tee
Paul S_3
Member Posts: 1,291
Hey everyone....I just got a job that involves diverter tees....the home has an existing diverter tee system....the home has sixteen radiators....eight on first floor and eight on second floor....the reason why we are gonna take out the existing main that runs the perimeter of the home is because the customer is converting the first floor and second to individual apartments....the customer does not want any construction done on any of the living areas so all the work will be done in the basement ....the existing main would be taken out and the pipes going to the radiators will stay....so the customer wants two individual boilers but leave the radiators....so we are gonna run two separatediverter tee systems in copper...my question is to determine pipe size...should I use a 20 delta tee?....and original main its 1 1/4 will I be able to use smaller pipe if the formula calls for it?....thanks Paul S
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
347-692-4777
ASMHVACNYC.COM
Apartments
Are each of the apartments going to have their own thermostat?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
yes
There are two floors.....each floor will get there own boiler...with eight radiators connected to each thanks Paul SASM Mechanical Company
347-692-4777
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Have yo suggested btu meters instead
of two boilers. You could zone the system and still use one boiler and then bill each tenant accordingly. Chicago now requires building owners to give information about utilities cost to potential renters so they can compare rents of units that include heat with ones that don't. The centrally heated buildings are nearly always going to be cheaper overall.There was an error rendering this rich post.
To answer your questions
Yes, I would use a 20 degree delta tee, figure out the BTU's of each unit and size the mains accordingly. It will probably come out to something less than 1-1/4 bacause you're dividing the load.
If you have enough money in the job, I would pipe it with a 2-pipe, reverse return system. A diverter tee system is notoriously difficult to purge.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0