dry charged condensor changeout
billboy
Member Posts: 1
When you can not find a new R410 coil to fit above a oil furnace and existing coil has a orifice control .Can that be used? thank you for any input
R-22 Dry Units
You are putting yourself and the equipment in a tough situation with any type of fixed metering device. Quality-driven makers of the dry units assume you will be using a TXV. You have possibilities from the easy to the extreme: (1) Locate an R-22 coil that will "match" the unit you propose; (2) Remove the orifice and pipe in a TXV; (3) Check other makers to see if they have an "N" coil that may be less tall; (4) Determine if the furnace is approved for horizontal application and change the configuration, or; (5) Replace the furnace, giving your customer higher efficiency, the advantage of R-410A, and the long life expectancy that comes with AHRI certified combinations.0 -
short coils
Some ADP and Aspen coils are pretty short and AHRI rate with a new 410 13 SEER machine. Often TXV is required. But sure beats the compromised SEER and capacity of putting a dry 13 SEER on some old coil.0 -
m-coil
Allstyle coil out of houston tx has m-coils that are 15.5" high. i've been selling them for a couple of years now in ct. and have had no problems. you have to buy a seperate txv for either 410a or r22.0 -
Short Coils
This is great news; thanks!0