gas pressure
 
            
                
                    Paul S_3                
                
                    Member Posts: 1,289                
            
                        
                
                                    
                                  in Gas Heating             
            
                    What is normal incoming gas pressure at the inlet of a gas valve...?...is 6"of water column to high?                
                ASM Mechanical Company 
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
0                
            Comments
- 
            In DC
 It's 5 to 7"0
- 
            6 sounds good to me
 we see NG 4.5 to 6.5, LP around 11...0
- 
            press.
 5-7" is correct as U.J. said for nat. gas. Most Gas co. dont supply over 7", In residential gas equip a min. of 5 " must be seen ahead of diaphram type gas valves for them to operate correctly as they depend on a press. drop to work, On commercial boilers etc it is better to have at least 6 " for good pilot press. Pressures over 1lb (28" ) can damage most gas valves,There was an error rendering this rich post. 0
- 
            It depends on the system
 If you are in an area that still has low pressure inner city (cast iron mains) distribution systems it can range from 4" W.C. to 10" W.C. as there is no regulator. That would be the pressure at the inlet of the gas valve. The main burner on all heating valves is regulated to around 3.5" W.C. to 4" W.C. at the outlet on natural gas. Most gas valves allow for about a 1" W.C. loss through the gas valve. That means anything less than 4" W.C. at the inlet is not going to give full 3.5" W.C. at the outlet. Keep in mind by the way all pilots are on line pressure they are not regulated.
 On high pressure system (a regulator ahead of the meter) the pressure out of the regulator is 6" to 7" W.C. depending on location.
 ON LP gas pressure out of the second stage regulator is 10" to 11" W.C. and typically 10" W.C. at the outlet of the gas valve.
 Hope that helps.0
This discussion has been closed.
            Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 112 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements