converted oil to gas
 
            
                
                    jimw72                
                
                    Member Posts: 4                
            
                        
                
                                    
                                  in Gas Heating             
            
                    i recently converted 3 boilers from oiled fired to gas fired using the ez carlins gas bruners on 2 of the boilers( both well mcclains) and a G3B burner on a utica boiler Starfire 3 model. The 2 ez carlins are running fine but i have received a question regarding gas usage on the utica. While the 2 ez carlins installs showed a 2/3rds increase in gas useage, the utica gas usage has tripled if not 4X creating a massive gas bill. Any thoughts on why or if there is some solutions. All boilers are steam boilers and were all cleaned and soot  vacced.                
                0                
            Comments
- 
            Burners
 Did you install a draft control? Did you match the existing BTUH input? What were your combustion numbers?0
- 
            i didn't
 even know they still made the g3b. i havn't needed parts for any ever so...0
- 
            I wouldn't have used the G3B on that Starfire-3
 it needs more static air pressure than the G3B can produce. That's why the original Beckett burner on these boilers is an AFG rather than an AF- the AF doesn't produce the static air pressure that the AFG can.
 Swap the G3B for an EZ-Gas, with the proper air tube for that boiler, and it'll run much better.All Steamed Up, Inc.
 Towson, MD, USA
 Steam, Vapor & Hot-Water Heating Specialists
 Oil & Gas Burner Service
 Consulting0
- 
            thx
 ok lemme give that a try0
- 
            yes
 yeah has a draft control....combustions numbers are 9.7 co2........3.6 o2....stack temp at 574f with 27% EA...and i matched existing btu from boiler to the burner and drilled the orifice accordlly0
This discussion has been closed.
            Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 112 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements