converted oil to gas

jimw72
jimw72 Member Posts: 4
i recently converted 3 boilers from oiled fired to gas fired using the ez carlins gas bruners on 2 of the boilers( both well mcclains) and a G3B burner on a utica boiler Starfire 3 model. The 2 ez carlins are running fine but i have received a question regarding gas usage on the utica. While the 2 ez carlins installs showed a 2/3rds increase in gas useage, the utica gas usage has tripled if not 4X creating a massive gas bill. Any thoughts on why or if there is some solutions. All boilers are steam boilers and were all cleaned and soot vacced.

Comments

  • JStar
    JStar Member Posts: 2,752
    Burners

    Did you install a draft control? Did you match the existing BTUH input? What were your combustion numbers?
  • pipeking
    pipeking Member Posts: 252
    i didn't

    even know they still made the g3b. i havn't needed parts for any ever so...
  • Steamhead
    Steamhead Member Posts: 17,385
    I wouldn't have used the G3B on that Starfire-3

    it needs more static air pressure than the G3B can produce. That's why the original Beckett burner on these boilers is an AFG rather than an AF- the AF doesn't produce the static air pressure that the AFG can.



    Swap the G3B for an EZ-Gas, with the proper air tube for that boiler, and it'll run much better.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • jimw72
    jimw72 Member Posts: 4
    thx

    ok lemme give that a try
  • jimw72
    jimw72 Member Posts: 4
    yes

    yeah has a draft control....combustions numbers are 9.7 co2........3.6 o2....stack temp at 574f with 27% EA...and i matched existing btu from boiler to the burner and drilled the orifice accordlly