heat pump t-stat

Options
Does anybody kn ow of a heat pump t-stat that will let you choose at what outdoor temperature you can stop the heat pump and run of either electric strip heat or gas back-up?

Comments

  • hheaddon
    hheaddon Member Posts: 10
    Options
    most of the better ones will

    Most of the better or well known brands can do this .they will need some kind of outdoor stat or air sensor to read the outdoor temps,that the stat will use to decide the changeover or the balance point,that is user set, to switchover the modes.Some brands will also use the outdoor temps to help control a humidifier setpoint and to lockout various operations of the heat and cool systems it is connected to. All this will be on the web to check out.If you plan on buying one at the big box stores.Check out the model numbers first!  Most of the cheaper off brands of t-stats will not support this option.
  • Techman
    Techman Member Posts: 2,144
    edited February 2013
    Options
    HP t'stat

    How about a 2 stage stat? 2nd stage controls the other type of heat w/ a relay , that brings on your aux heat and turns off the HP.This way when the HP can't supply enough heat 2nd stage brings your other heat on w/o an outdoor temp control.
  • John Mills_5
    John Mills_5 Member Posts: 951
    Options
    outdoor stat

    Need something with an outdoor sensor. Vision Pro, Prestige, some of the upper end White-Rodgers and Aprilaire. All will do that. Beyond them, I get nervous! But I guess that's good for biz
  • Techman
    Techman Member Posts: 2,144
    Options
    HP stat

    The stats w/ the outdoor sensor , isn't that just for showing the outdoor air temp? As compared to controlling something?
  • John Mills_5
    John Mills_5 Member Posts: 951
    Options
    lockout

    Most stats with outdoor sensors do use that info for locking out equipment. The Honeywells, Vision Pro, Prestige, will use the sensor to lockout the compressor in bitter weather or lockout the strips in mild weather. Some will use the sensor to adjust humidity level on a connected humidifier to as not to get too humid in cold weather. 
  • unclejohn
    unclejohn Member Posts: 1,833
    Options
    Carrier has

    A real nice two wire tstat that will do what you need. Mod. tp-prh01-a.