under size steam header
dwh54
dwh54 Member Posts: 1
what will happen when you under size your boiler header have a boiler with 2 5inch risers off of boiler they go into a 6inch header boiler manufacure wants a 8inch header
    Steamhead Member Posts: 17,837
    You'll have a LOT of problems
    wet steam, high fuel consumption, uneven heat, banging, water-level problems in the boiler........
    Do it right. Change the header.
    Consulting
  • pipeking
    pipeking Member Posts: 252
    yea
    u got to do what the manuf. want if u ever have problems down the road, but 8" does seem excessive. 2- 2.5" pipes don't even come close to 1- 6" flow rate, so what is it based on?
  • MTC
    MTC Member Posts: 217
    That's 2) 5" risers,
    which makes sense for an 8" header. Must be a pretty large building...
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,417
    wet steam poor heat
    2.5 x2.5x 3.1416x2 = 39.27
    3x3x3.1416= 28.27
    4x4x3.14=50.26
    You need the 8" header.
    cell # 413-841-6726
  • MTC
    I agree with your conclusion Charlie,
    but not sure I understand what you mean by your math. Can you explain further please?
  • pipeking
    yes charlie please explain...
    this is my math, if i'm wrong i need to know where
    the radius of a 2.5" pipe is 1.25"          and the radius of a 6"pipe is 3"
    1.25x1.25x3.14=4.90sqin +                        3x3x3.14=28.26sqin
                       = 9.8sqin
    i can't get it to stop underlining!!!   but i'm pretty sure that u add the area off the two 2.5" risers to get the tottal area of the two, but if i'm wrong and you multiply them together it's still only 24.01sqin.
  • MTC
    Oh, I think I get what you're saying Charlie...
    The area of (2) 5" risers is Pi*Rsquared = 3.14*2.5squared, times 2 risers = 39.27
    The area of the current 6" header is PiRsquared = 3.14*3squared = 28.27, which is too small
    The area of the spec'd 8" header is PiRsquared = 3.14*4squared = 50.26, which is larger than the total area of the 2 5" risers.
    The minimum header size would be slightly larger than 7", which means you need an 8" header.
    it is two 5" risers pipeking not
    two 2 1/2" risers. we are in the big leagues now boys.
    cell # 413-841-6726
  • SWEI
    SWEI Member Posts: 7,348
    and you can drop the π
    anytime you are comparing round pipes.  Squaring either D or R will give you the answer.
    I kept in Pi to show
    the actual area diffrence not ust the proportional  difference. If the numbers differ by larger amounts it seems to make the problem more visible. When comparing in my head I leave out the Pi. Unless it is right after supper then I have the pie if it is there to be had.
    cell # 413-841-6726
  • pipeking
    I NEED GLASSES!!!
     i could have swore it said " how would u size a boiler with 2.5inch risers" i thought there was a decimal point.!! you got it, whoaoawhoa, you got it!! we're in the big leagues now!
  • MTC
    Good point...
    multiplying all variables by the same constant does just give you more messy math. I hadn't really ever thought about it.
    I'm kind of anal though, and I think seeing the real numbers, not just proportional numbers, somehow makes me happier, whatever that means.
    What about pi FOR dinner?
    edited February 2013
    Pie for dinner
    Pot pie or Steak and Kidney? The kidney in steak and kidney pie is beef kidney not kidney beans so you should be good.
    cell # 413-841-6726
  • MTC
    can't do kidney beans... but pot pie is all good :)
