New steam boiler has unwanted vacuum
I just replaced a Weil Mclain LGB-7 that had 5 cracked water jackets. Replaced with the exact same gas steam boiler. System has pressure-trol controls. Upon startup the system will not gain any pressure. Has only vacuum. Neither I nor my company has experienced this before. From the research I have done, at some point in history this building had a Bromell system and was coal fired. The steam venters that are installed are 1A and there are 3 of them throughout the building. Any help or suggestions would be greatly appreciated.
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,919
    There's got to be more to this.
    Is there a vacuum pump? Are you getting any steam out of the boiler? Is this a one-pipe or two-pipe system?
    What kind of vents are you talking about? Hoffman 1As are angled 1/8" radiator vents. Are you saying these are the only vents in the system? Where are they located?
    It might help if you could post some pictures.
  • SWEI
    SWEI Member Posts: 7,342
    Broomell system
    http://www.heatinghelp.com/files/articles/1383/54.pdf is worth a read.  Are the original  trapped union elbows still there?
    I'd love to see that "Combined receiver, Draft-regulator, Gauge, and Relief Valve" in person.