pressuretrol on burnham V9a
hello my Burnham v9a has two pressuretrol boxes on it, would like to know where setttings should be. pressuretrol on left has diff @ 2.5psi and main @ 5psi. right pressuretrol only has main which is set @ 7psi
    Jamie Hall Member Posts: 27,305
    Try...
    changing the left one to a differential of 1 psi and a cutin of 0.5 psi if it is additive, or a cutout of 1.5 psi if it is subtractive.  Leave the other one at 7.