Zone Problems

Jaybird845
Jaybird845 Member Posts: 8
I recently added a zone to my oil heat boiler. The thermostat is set for 68 and the room temp is 63. If I turn the thermostat up to 70 I hear a click the zone valve opens. The radiators get hot. The zone runs for a little while. Shuts off before the thermostat even gets up to 70. All the other zones operate fine.

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • billtwocase
    billtwocase Member Posts: 2,384
    pics?

    thermostat, and location?
  • Jaybird845
    Jaybird845 Member Posts: 8
    Zone Problem

    The zone is an upstairs bedroom. It is a Honeywell thermostat located in the room that is cold. It is away from the baseboard heat on an inside wall. It is not near windows or in a drafty area.
  • billtwocase
    billtwocase Member Posts: 2,384
    what model

    honeywell thermostat? 
  • Jaybird845
    Jaybird845 Member Posts: 8
    Thermostat

    CT87K
  • billtwocase
    billtwocase Member Posts: 2,384
    t87k

    is a terrible thermostat. Among the worst. Go with the digital Pro-1000. everything else, from what I can see, looks OK.
  • Jaybird845
    Jaybird845 Member Posts: 8
    Thermostat pic

    Here is a picture of the thermostat with the setting of 68 and the room temp of 63. Not calling for heat
  • Jaybird845
    Jaybird845 Member Posts: 8
    Thermostat

    It is the same thermostat I have everywhere in house
  • billtwocase
    billtwocase Member Posts: 2,384
    you can check

    the dip switches in the back, but more often than not, we would change out 3-4 of these things until one would stay within a couple of degrees of where it was set. I have had them off as much as 10 degrees. This was a hurry up replacement for the T87 mercury thermostat. Still unbeatable in my eyes. 
  • Jaybird845
    Jaybird845 Member Posts: 8
    T87

    Ok i was mistaken about my other thermostats. They are T87 mercury type that you mention. I have remove one of these and put in the problem area. I will see if that works. I have dipswicth 1 off and 2 on for hot water baseboard on the CT87K
  • billtwocase
    billtwocase Member Posts: 2,384
    sounds like a plan

    The old T87 base plate needs to be level. 
  • Jaybird845
    Jaybird845 Member Posts: 8
    T87

    The T87 seems to be working. The room temperature is still not up to the temperature set on the thermostat, but at least it is within 2 degrees. I have the thermostat set on 70 and the zone shuts off at 68. Weird. I did level the thermostat.
  • SWEI
    SWEI Member Posts: 7,348
    another validation of the original T87

    So I have to wonder - is there some country where they still allow mercury switches in which Honeywell has a presence?
  • Jaybird845
    Jaybird845 Member Posts: 8
    Still not working right

    The heat is coming on and flowing, but shuts down before the room gets up to temperature. I don't know why this is happening.
  • heatpro02920
    heatpro02920 Member Posts: 991
    Bad thermostat...

    I would change that thermostat out, if the problem persists but an ohm meter on the 2 wires and watch it stop calling, if the ohm meter is buzzing with continuity after the zone closes than it is a zone valve head problem.... But my money is on t-stat problem....
  • billtwocase
    billtwocase Member Posts: 2,384
    not the thermostat

    They can be calibrated. 