MONOFLOW GPM
smklin
Member Posts: 69
How many gpm does a monflow system require . Have a system that has about 385 feet of baseboard 7 unit appartment . 6 zones per unit.
If your baseboard
output is 500 BTU/foot and you design for a 20 degree temperature drop, that's an output of 192,500 BTU with a flow rate of 19.25 GPM.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Gpm
Depends on the heat loss and required BTUH's.0 -
Really?
42 zones and 385 ft of baseboard? Monoflo?0 -
There may be more to it than temperature drop
Such as, min and max flow through the venturi tees in order for them to work properly. I remember seeing discussions about this but I didn't retain what it was.0 -
Main Size:
Which probably needs a 2" main size unless or until you branch off to individual circuits to the separate units.0 -
FLOW
That is what i thought to ask .What is the flow to make the venture tee's work. Have a lot of air problems. Thanks to all.0 -
Flow:
Sounds like it is time for a big ECM circulator?0 -
PAUL
i was thinking the same thing!0 -
There's a lot to this.
This is from the Library: http://www.heatinghelp.com/files/articles/955/281.pdf
Read up on it before you do anything else.Retired and loving it.0 -
Gotta Love
Those all books..Saved that one to the files..Thanks Mr. H. Will have to get together next month at the amusement park.There was an error rendering this rich post.
smklin
I am interested in how this was zoned. Could you make a simple drawing of one zone and post it?0 -
Lots of good stuff in that Library.
It pays to wander off the Wall. ;-)Retired and loving it.0 -
B&G Handbook
I got so much out of it that I actually bought a 1949 hard copy on eBay. If you're patient, they can be had for under $10 shipped.
Thanks, Dan!0 -
That book
is how I first learned about hydronics. I went to work for the rep. They say me down with that book and said, "Read."
It was good advice. I've been reading ever since.Retired and loving it.0