MONOFLOW GPM
smklin
smklin Member Posts: 69
How many gpm does a monflow system require . Have a system that has about 385 feet of baseboard 7 unit appartment . 6 zones per unit.
  • If your baseboard
    output is 500 BTU/foot and you design for a 20 degree temperature drop, that's an output of 192,500 BTU with a flow rate of 19.25 GPM.
  • JStar
    JStar Member Posts: 2,752
    Gpm
    Depends on the heat loss and required BTUH's.
  • Paul48
    Paul48 Member Posts: 4,469
    edited February 2013
    Really?
    42 zones and 385 ft of baseboard? Monoflo?
  • Gordan
    Gordan Member Posts: 886
    There may be more to it than temperature drop
    Such as, min and max flow through the venturi tees in order for them to work properly. I remember seeing discussions about this but I didn't retain what it was.
  • icesailor
    icesailor Member Posts: 7,260
    Main Size:
    Which probably needs a 2" main size unless or until you branch off to individual circuits to the separate units.
  • smklin
    FLOW
    That is what i thought to ask .What is the flow to make the venture tee's work. Have a lot of air problems. Thanks to all.
  • icesailor
    Flow:
    Sounds like it is time for a big ECM circulator?
  • pipeking
    pipeking Member Posts: 252
    PAUL
    i was thinking the same thing!
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,686
    There's a lot to this.
    This is from the Library: http://www.heatinghelp.com/files/articles/955/281.pdf
    Read up on it before you do anything else.
    Retired and loving it.
  • CMadatMe
    CMadatMe Member Posts: 3,086
    Gotta Love
    Those all books..Saved that one to the files..Thanks Mr. H. Will have to get together next month at the amusement park.
  • Paul48
    smklin
    I am interested in how this was zoned. Could you make a simple drawing of one zone and post it?
  • DanHolohan
    Lots of good stuff in that Library.
    It pays to wander off the Wall. ;-)
  • SWEI
    SWEI Member Posts: 7,348
    B&G Handbook
    I got so much out of it that I actually bought a 1949 hard copy on eBay.  If you're patient, they can be had for under $10 shipped.
    Thanks, Dan!
  • DanHolohan
    That book
    is how I first learned about hydronics. I went to work for the rep. They say me down with that book and said, "Read."
    It was good advice. I've been reading ever since.