honeywell burner control - alarm light on
elfie
Member Posts: 266
anyone ever resolved issues with the honeywell burner control device? its a series 7800 relay module
it is used within a powerflame burner as part of a hot water boiler (15 section cast iron boiler)
the alarm light has occasionally started flashing and shuts down the burner from cycling on. a simple pushing of the reset solves the problem.
any idea what could be the problem? and how to figure out problem - have heard this device might have an event memory that can be accessed for diagnostic purposes.
thanks
thanks
It
appears that you need to purchase additional equipment and or software to access the info. http://lattnerboiler.com/Honeywell%20Technical%20Literature%2065-0229-1.pdf
https://customer.honeywell.com/resources/techlit/TechLitDocuments/65-0000s/65-0114.pdf0 -
module
You will need the S7800A1142 keyboard display module. Unfortunately they cost around $300.00. When i would update old RA890 controls to RM800's i would always include in my quote the cost of the S7800 keyboard so the customer would have it At least 80% of all failures are due to flame rectification problems so make sure you have a good strong pilot and your pilot is not rusty. Also make sure your connections are good and you have a good ground where it is called for.There was an error rendering this rich post.
need for cleaning burner
how frequently should the powerflame burner be cleaned when it uses natural gas? and what types of things get done.
thanks0 -
p/m
Contact Powerflame they have a great tech dept or download I.O.MThere was an error rendering this rich post.
p/m
tripping one of the shut downs
You are tripping one of the shut-downs. It could be a number of things such as low gas pressure/high gas pressure. Something in its annunciation sequence is tripping. A low O2 will cause flame fail and controller will shut down on flame fail. If you had the display module to hook to the controller it would tell you which lockout you are having.
You can also call Exotherm, they are a Houston based company that does burner control service. http://www.exotherm.com/
or call them at 713-981-91000 -
Or maybe:
Or maybe a safety device in the gas train. Get the control. Its worth the money.0
- 110 Chimneys & Flues
- 981 Plumbing
- 387 Solar
- 17 Recall Announcements