my first drop header install EGH-85
Motty
Motty Member Posts: 8
hi all,
Pics of EGH 85 install. Any feedback is appreciated.
Thx
Motty
  • JohnNY
    JohnNY Member Posts: 3,339
    That's one way to do it.
    Looks pretty ok considering you kept the old header. You should add a valve to your Hartford Loop, though. And you need a skim valve.
    Well done overall.
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • Motty
    edited January 2013
    Valves
    John,
    I have a nipple and cap on the right side for skimming ( already skimmed the boiler). Why do recommend a valve on the Hartford loop? What is the advantage?
    Thx
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,919
    edited January 2013
    Not speaking for John here
    but a valve on the Hartford loop lets you drain and flush the boiler or the return without having to drain the other to the level of the Hartford. It will also allow you to flush more gunk out of the mud leg when you open that drain on the bottom of the equalizer by preventing the condensate from the return from flowing down and washing it back into the boiler.
    And, by the way, nice job. I think the tricky ones like this show the most skill and creativity.
    Steamhead Member Posts: 18,187
    I've built headers like that
    when there was no other way to get both steam supplies on the same end of the header.
    Nice work.
    Consulting
  • JStar
    JStar Member Posts: 2,752
    Header
    Not bad. We just did something similar on a repiping job. As long as the pitch and assembly is right, it should work great.
  • gerry gill
    gerry gill Member Posts: 3,083
    well done!
    I like it. I think you did a nice job. Welcome to the drop header club!
    gwgillplumbingandheating.com
  • Motty
    thanks
    thank you for the kind words and advice.
    motty