McDonnell 101 a
Tom E
Member Posts: 15
I have a water feeder that will not feed....I cleaned the filter but nothing. The feeder engages but no water to boiler unless I manually feed. It looks like an older model, pre 1995 with no cartridge to replace. Any suggestions...I thought cleaning the filter would do it and it was really filthy but no good. Thanks
101-A Water feed.
Hi Tom; if you can man feed the control then it's not a strainer/filter problem. I am assuming it's 24vac solenoid. I know you checked this, but do you have 24vac to the solenoid? if you have power and the solenoid will not open, the coil is dead. The only other problem to look at is, see if the LWCO is closed providing the power to the solenoid. Let me know how you make out. You said it engages the feeder, what exactly do you mean? Are you hearing a click?
Mike T.0 -
101a
You can hear the click of the relay? And the button on top goes in, but no water goes thru the valve. It will stay engaged until I add water manually. It is 115 volt, not 24 VDC. Thanks for your advice. If I drain the lo water cutoff, the feeder clicks on right away.0 -
Prior problem...
Not saying that this is your problem, but one time I had a valve that would not completely shut down. Turns out the problem was that the 75 psig pressure would not let the valve stem re-seat. I am wondering if this may be the same except not allowing it to pick up. Shut the valve down virtually all the way the re try. Just a thought.