Boiler size
cdm
Member Posts: 77
My steam radiators egual 206 sq. ft. of radiation area, from my figures I need a 50K BTU boiler. Do I need to to increase the net output of a boiler by 1/3 to compensate for piping loss, to have a properly size boiler.
thanks -chuck mulford-
No
That's how they arrive at a net output. You match the net to your total EDR.0 -
sizing
look for removed radiators and take into account their piping. It affects pick up factor.Gennady Tsakh
Absolute Mechanical Co. Inc.0 -
Reply to boiler sizing
Thanks - I appreciate your quick response, and will size my boiler accordingly.
cd mulford0 -
Boiler sizing
Thanks for your response - I did remove one (6) section radiator in my kitchen - I will include the extra EDR in my boiler selection - thanks
cd mulford0 -
removed radiators
No you do not have to add them. what you do is add 1/4 edr of removed radiators, just to account for existing piping to non existing radiators.Gennady Tsakh
boiler sizing
Thanks for the info. I will thake this lesser amount (1/4 EDR) into account.
cd mulford0