My steam radiators egual 206 sq. ft. of radiation area, from my figures I need a 50K BTU boiler.  Do I need to to increase the net output of a boiler by 1/3 to compensate for piping loss, to have a properly size boiler.
thanks -chuck mulford-
  • Paul48
    Paul48 Member Posts: 4,469
    No
    That's how they arrive at a net output. You match the net to your total EDR.
  • gennady
    gennady Member Posts: 840
    sizing
    look for removed radiators and take into account their piping. It affects pick up factor.
  • gennady
    edited December 2012
    duplicate
    duplicate
  • cdm
    Reply to boiler sizing
    Thanks - I appreciate your quick response, and will size my boiler accordingly.
    cd mulford
  • cdm
    Boiler sizing
    Thanks for your response - I did remove one (6) section radiator in my kitchen - I will include the extra EDR in my boiler selection - thanks
    cd mulford
  • gennady
    removed radiators
    No you do not have to add them. what you do is add 1/4 edr of removed radiators, just to account for existing piping to non existing radiators.
  • cdm
    boiler sizing
    Thanks for the info. I will thake this lesser amount (1/4 EDR) into account.