Boiler size
cdm
Member Posts: 77
My steam radiators egual 206 sq. ft. of radiation area, from my figures I need a 50K BTU boiler. Do I need to to increase the net output of a boiler by 1/3 to compensate for piping loss, to have a properly size boiler.
thanks -chuck mulford-
thanks -chuck mulford-
0
Comments
-
No
That's how they arrive at a net output. You match the net to your total EDR.0 -
sizing
look for removed radiators and take into account their piping. It affects pick up factor.Gennady Tsakh
Absolute Mechanical Co. Inc.0 -
-
Reply to boiler sizing
Thanks - I appreciate your quick response, and will size my boiler accordingly.
cd mulford0 -
Boiler sizing
Thanks for your response - I did remove one (6) section radiator in my kitchen - I will include the extra EDR in my boiler selection - thanks
cd mulford0 -
removed radiators
No you do not have to add them. what you do is add 1/4 edr of removed radiators, just to account for existing piping to non existing radiators.Gennady Tsakh
Absolute Mechanical Co. Inc.0 -
boiler sizing
Thanks for the info. I will thake this lesser amount (1/4 EDR) into account.
cd mulford0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements