Oil Burner Reset Tripping
JeremyN
Member Posts: 15
We've got a Weil McClain gold oil boiler here hooked up to a steam system. We just came home from a week away and realized that our house was way below the thermostat's set point and nothing would turn on the boiler. I went downstairs and hit the reset, and the burner turned on. Problem solved... That was until a few minutes later when it shut off again. I repeated this step, noticing that the whole time there was fire in the chamber. After the second time, I bled the pump in case there was some air in there somehow and that seemed to do the trick. We went through a number of burner cycles (about 2 hours worth of firing) and I was convinced I had solved the problem.
This morning I woke up and again the house was way below the set point. I went through the same step of bleeding, and again the burner worked for a number of hours. Just now, I noticed the problem again, and this time all I did was hit the reset button and the burner has been firing for a good 40 minutes without any signs of stopping.
I'm at a loss for what's going on here. The bleeding seems to be a red herring as this most recent time didn't require it. We're about to get our system swapped out for gas so I wouldn't be too worried about it except for the fact that we're heading out for New Years tomorrow and won't be back until Tuesday - we've just had this one day home with the problem sandwiched between trips. I'm pretty worried about leaving the pipes (and cat) in a potentially freezing cold house.
Any ideas for a quick fix?
Thanks,
Jeremy
Thanks,
Jeremy
Maintenance
When was the last annual service done?
There are too many things to list. You need to call a tech.Bob Boan
As Iron said
we could give you a shopping list of probable causes, but you should hire a pro.0 -
Oil boiler
As said it could be a number of things.
Call a tech.
It could be a weak cad cell or high voltage transformer. Burner lights the first time but not the second. It could be blocked oil flow due to a plugged oil filter or nozzle.
could be a few other things that are less probable.0 -
thanks guys
Our annual service was done in September. Is that something they should have looked at? Should I call the guy back?0 -
YES
Call them back. Just make sure that if you reset it AND it doesn't fire - DON'T reset it again.0 -
reset tripping
Where do you live?
If you live near me, I can help you............... Springfield, Massachusetts0
- 123 Chimneys & Flues
