how do I know how many btus a pipe will carry?
Mitch_5
Member Posts: 102
the Golden Rules of Hydronic Heating has some good rules of thumb in the HW section page 64 on and for free not to knock day because you should have all his books as do I. But Burnham has a pocket book you can get from there distributors that has similar charts.
Mitch S.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=388&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
Mitch S.
How can I determine how many btus any given pipe size will carry at specific temperature drops?0 -
depends...
on flow rate, pipe diameter and temp. drop end to end..detlta T...
Generaly speaking..1/2 is 15K (1.5 gpm), 3/4 40K (4gpm), 1" 80K (8gpm), 1.25" 140k (14gpm)...20 temp drop...
right. and thank you.
but where can I find a chart to calculate it as my DeltaT shifts?0 -
System Syzer
B&G has a System Syzer. You can go to thier web site and download it.
Tim D.
BTU cap of pipe
This may help
Ed Carey0 -
dT
It is important to remember that there is nothing magic about a 20 degree delta-T. It just makes the math easy.0 -
type of fluid and temperature also plays a part
I use the Pipe Sizer program in Siggys HDS software. IT allows you to play what ifs with delta T glycol solution, temperatures, etc. With every input a chart appears showing the velocity in FPS so you can see where you have room to push some additional flows.
1" copper can easily move 140 degree water, 180,000 BTU/hr at a 35 deltaT 10.8 gpm at 3.8 fps velocity 2psi pressure drop per 100 feet of tube.
hot rodBob "hot rod" Rohr
Question?
I have a 3/4" line about 100' from meter that I want to connect a 24" fire ring for fire pit and two 12" fire rings for fire bowls. Is 3/4" sufficient and how many BTU's can it support?0 -
This thread....
Is about hot water in a pipe. You question is about gas?
I would suggest starting a new post. You will need a description of what the pipe sizes and lengths are as well as the btu sizes of all the appliances. The system gas pressure would also be needed.
Albert Einstein1 -
Water verses gas
Your post is referencing gas pipe sizing. This thread is in reference to btu carrying capacity of pipe filled with water, or glycol mix.
Is this for lp, or ng?
If ng 100' will supply 68000 btus about the average sized BBQ grill.
If lp 100' will supply 162000 btus.
BUT... What is the 3/4" line that is existing supplying gas to?
If it supplying other appliances such as furnace, boiler water heater,BBQ,dryer etc. you have to account for that. Not as easy as tapping into that line for doing what ever you want.
The bottom line is one of the appliances will starve for gas if it fires up, and the fire rings are in operation.0 -
Pipe Carries GPM
The universal answer is, it depends. Pipe carries gallons per minute not a flat btu/hr. Btu/hr delivery utlizing a particular pipe size is predicated on the system delta-t.
GPM = Btu/hr / (Delta-T x 500)
As some have posted, there are maximum recommended gallons per minute for each pipe size.There was an error rendering this rich post.
Gas
He is trying to size a gas line."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Pipe Sizing Guidelines
2-4 GPM=3/4"
4-9 GPM= 1"
8-14 GPM= 1 1/4"
14-22 GPM= 1 1/2"0 -
Trampled
If you have a specific question, please start your own thread. That way someone elses question doesn't get lost in the shuffle.0
- 120 Geothermal