furnace firing issue
LB_481
LB_481 Member Posts: 4
furnace is only firing the first 3 burners,it goes out on flame sensor saftey.any ideas on why the last burner would not fire??
  • RJ_4
    RJ_4 Member Posts: 484
    Gas
    Have  a licensed Hvac contractor check it.   could be low gas press. you could start with your gas co.   alot of them dont charge to check your furnace.
  • LB_481
    thank you RJ going to check gas pressure today ill post the result.
  • RJ_4
    pressure
    You need a minimum of 5 inches water column to inlet of most gas valves and 3.5 inches to burner on most  furnaces,  these setting can change if you have a 2 stage valve and on commercial burners. most diaphram style gas valves depend on this 5inch to 3.5 inch pressure drop to operate correctly.
  • Steve Whitbeck
    Steve Whitbeck Member Posts: 669
    Dirty burners
    Could just be a dirty cross over on the burners.