Boiler Repipe - OR- Better Venting
I've had some trouble with pressure and balance with my one pipe system. I put a couple of posts here and received very helpful advice. (Thank You). The main issue has been that there is at least one random radiator that does not get heat during each cycle AND that at the end of the mains, the vents (2 Gorton #2's) don't get enough heat/steam to ever close. Therefore, the boiler never builds any pressure showing on the 1 - 3 lbs gauge.
BUT...some of you helped me realize that 1) there was an issue with the near boiler piping (the header was reduced to 2" when the manufacture called for 2 1/2". I ordered the proper sized fittings to make the change ....BUT....I also learned that I had been over venting the radiators by quite a bit - thus the main vents never got enough heat/steam.
Now that I've fixed the radiator venting, all the above mentioned problems have vanished and the system is working very well. Given this, should I still redo the near boiler piping to accommodate for the 1/2 difference in header pipe sized.
I've attached a photo.
As always, thank you for your help.
  • Enreynolds
    Enreynolds Member Posts: 119
    If it were me
    Now that the venting has been sorted out, and the system is running well, AND it is November 28th, I would put off the boiler re-pipe til the spring.  This way you don't have to worry about Murphy taking your boiler down for a week in the dead of winter.
    Eric
  • Paul48
    Paul48 Member Posts: 4,469
    Tee'd Main
    You will be also splitting that tee'd main in the spring?
  • Jeff_44
    Jeff_44 Member Posts: 94
    Yes -
    I plan to put a drip connection from the main down to the wet return. Does that make sense?
  • Paul48
    edited November 2012
    No
    Three main risers......no tee'd mains. http://www.comfort-calc.net/Steam_Piping_Donts.html
  • Jeff_44
    There is a ...
    Capped end to this main...as seen in the photo. Would it be best to tie in there?
  • Insulation
    Don't forget to put some insulation on the pipes, and because you will be reworking them in the spring, I would wrap them with fiberglass roll insulation, about 2 inches, as it is less effective than real preformed pipe insulation, (which you can put on when the re-piping is done).--NBC
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,919
    Insulation
    NBC's suggestion is right on the money. Loosely wrapped fiberglass insulation will do a decent job of insulating for now, and later you can use it to wrap the fittings and tight spots where the pipe wraps won't fit.
  • Jeff_44
    Thanks
    Actually,
    the photo is from the day of instillation about six years ago. The contractor did a beautiful job of wrapping all the near the boiler piping. He did not insulate the the equalizer - Is this typical?