zone valve question
cf
Member Posts: 3
Have a taco 3 wire valve on geothermal system would like to replace with honeywell v8043
wondered if anyone had tips on the wiring to make it easy.
any response greatly appreciated.
2-wire
3-wire powers the valve open and closed. The H/W is spring closed, so now you only use 2 wires to power it open.
Other factors may be involved though such as a signal from the 3 wire must be changed to end switch operation from the 2-wire valve head.0 -
are all 3 terminals used on the Taco?
Easy wiring. Your #1 on your taco will become TH on the H/W, #2 on the taco will become TR and jump it to the end switch terminal above it. #3 on the taco will be the other end switch terminal. The bottom far left terminal on the Honeywell is nothing, and not used. If there are only 2 wires on your Taco, the end switch will not have wires connected to it. Only TH and TR will be used, like an EK. Good luck0 -
Taco
That is not a power open/power close valve.
With the Taco valve You aply power to two of the terminals and this opens the valve - the third wire feeds power back to the heat pump to start the compressor.
The Honeywell valve may not have enough closing force to stop the water flow.
I would replace it with another TACO.0 -
thanks for the replies
plumbed in the hw and you were right won't close all the way. will be talking to the salesman tomorrow. and yes the taco uses all 3 wires and thanks for the how to on the wiring.0 -
system pressure
I believe the old taco valves were a slow opening globe valve design ( heat motor ) I believe the mh valve use a spring and rubber ball device, I would check both manufacts. for pressure drop and flow data There have been water hammer problems in the past if the wrong valve is installed. I agree with Steve.There was an error rendering this rich post.
Thanks for the advice
Where is a good place to buy the Taco valve.0 -
taco
most hvac supply houses should stock them Taco is a large manufact. of valves pumps etcThere was an error rendering this rich post.