A combustion Analysis question
KCA_2
Member Posts: 308
in Gas Heating
Hello All...
I have a Laars JVH160 Natural Gas (induced draft) Boiler with these readings.
CO2 5.8%
O2 10.7%
CO 25 ppm
Draft .07
Seems off... If I adjust the manifold pressure down from 4" the CO2 % goes down.. (Recommended by factory is 4.0") seems like the CO2 is low and the O2 is high... Draft should be in the negative... Stack temp was 287degF... I clocked the meter and everything worked out well... How do I get the readings in where they should be... CO2 around 6.5 anyway and O2 at 7-9%.... I don't know why the draft is in the positive...
A bit confused...
:-) Ken
CO2 5.8%
O2 10.7%
CO 25 ppm
Draft .07
A bit confused...
:-) Ken
:-) Ken
need to
Turn up your manifold pressure to raise the CO2 and the O2 willdecrease as well. You want to keep your CO under 100 ppm. CO2 on natural should be 8-9.5% and O2 6-9% for Natural gas or whatever the manufacturer says.0 -
CA
What draft meter do you have? Was it facing into the boiler or into the chimney? A positive draft could mean a blocked chimney.0 -
The unit has a total
of 5' of flue... Blows right outside the mech room... There isn't a blockage...
I can't turn the Manifold pressure up to much... I played a bit and turned it up to 4.5" and the CO2 went to 5.9 maybe... I couldn't leave the burner running that high though... There really isn't anything else to adjust...
I have a Bacharach Fyrite Pro
:-) Ken:-) Ken0 -
Laars
I don't think those burners have any adjustments.
Sounds like too much primary or excess air. With such a short amount of venting, I think the inducer is drawing too much air through the boiler. I probably shouldn't recommend this, but I would mess around with blocking off the exhaust a small amount at a time to see if the numbers change.0 -
wrong orifice
You might make sure the burners have the right orifice size,0 -
I'm at 6000' ASL
The unit has a # 47 DMS orifice... So maybe a smaller one?
The orifice clocks ok now...
Hmmmm...
:-) Ken:-) Ken0 -
burners
How many burners? I'm just under 6000' myself0 -
I believe 7
7 burners....
Why?:-) Ken0 -
adj. air shutters
With a #47 orifice you probably have 8 burners
After looking at a gas orifice chart with a #47 orifice you probably have 8 burners at 4. 0 w.c. If I remember right, the burners do have an adjustable air shutter. With your analyzer running, try closing the shutters a little bit and see if that brings the CO2 up while keeping the CO under 100 ppm
`0 -
Air Shutters
are wide open..... And I double checked... there are 7 burners...
with a 4" water manifold pressure recommended by the manufacturer... That doesn't add up..
:-) Ken0 -
Air
Meter down on the burner shutters. That will bring your O2 down.0 -
and
Like Jstar said your 02 will go down and your CO2 will go up.0
- 87K THE MAIN WALL
- 112 Chimneys & Flues
- 106 Geothermal
- 980 Plumbing
- 388 Solar
