Honeywell Supervent

Options
ddr
ddr Member Posts: 14
We are currently using Honeywell's Supervent PVU100 on our boiler installs.  We are happy with the results, however on a recent install we utilized the bottom tap of the supervent directly on top of a vertical riser pipe.  We had a reason to do this for space limitations but could not find data to support this.  Has anyone else done this with satisfactory results?



Thanks much,

Derek

Comments

  • Robert O'Brien
    Robert O'Brien Member Posts: 3,541
    Options
    Bottom tapping?

    You mean the 1/2" exp tank tapping? If so,waste of money. If you need a vertical air separator .http://www.spirotherm.com/datasheets/VJV-1B.pdf
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • ddr
    ddr Member Posts: 14
    Options
    Bottom tap

    The Honeywell supervents have a full port tapping on the bottom as well.
  • Ironman
    Ironman Member Posts: 7,376
    Options
    Depends on how it's piped

    If all of the system water is flowing through it, then it should effectively function as an MBR.



    If, however, it's connected to the top of a Tee and the system water is not flowing through it, then it will have about as much effectiveness as an auto air vent but it will not remove micro bubbles or dissolved oxygen.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • ColoradoDave
    ColoradoDave Member Posts: 54
    Options
    Bottom Tap

    The bottom tap on Honeywell Supervents is intended for the connection of the expansion tank.  The wire mesh (for the layman) inside the supervent is for collision and adhesion of the air bubbles in the system.  If the supervent doesn't see the flow then the mesh can't do it's job.