Convectors not getting hot
paplumber
Member Posts: 1
Installed new boiler, with 2 zones, one zone is baseboard loop for small addition that I have purge valve at the end of loop, this zone heats fine
main zone is rest of house that has convector that have to be purged separate.
Is a 2 pipe system direct return, that is a loop around the whole basement, convectors at end of loop are not getting hot, I have honeywell supervent and I'm pumping away from expansion tank, Have Taco 007 circulator do I need bigger circulator?
have you??
Are you able to "power purge" the zone using the fill valve or a hose connected to a boiler drain? It sounds like you are air locked.
Albert Einstein0 -
Cold Convectors:
Did you bleed the air from the convectors? Convectors aren't usually series looped. If the hot water is going around the main, and the "convector" isn't getting hot, it probably needs to be manually bled. "Purging" won't vent it.0
