Buderus Pressure
JoeBags
Member Posts: 5
in Gas Heating
Hi. My GB142 system has low pressure. When it was first installed, the installer showed me how to increase the pressure should I ever need to, but I've forgotten. I've attached a picture. Thanks for any help!
Low Pressure
I'm having the same problem. It's not always low but the "H7" or "P13" shows up a lot on the control panel.0 -
Error Code
My understanding is that the H7 is the error code for low pressure. The P is your current pressure. Yours is 13. Mine is 3 - which is so low the system won't even come on.0 -
H7
You have a leak. You should never have to fill the system after the installation.0 -
Done
Never, Never
Just add water to the system without determining how it found its way out of the system. It did not just disappear.There was an error rendering this rich post.
Hmmm
Signs of leaks in the photo.0 -
There should be a spiket
fill valve on your line. On my GB142 I have a washer hose attached to one spiket with new water connected to the other spiket on the line running into the boiler.....this is how I fill mine whenever I need to....also, I've had mine for 7 years, it will need an occasional fill....0 -
Mplsavant Correct
Yes. Plumber said my system has an auto-fill valve that got stuck, so it was just a matter of a manual flick of the valve to over-ride. No, no leaks. Heating system not even on, just hot water. Plumber tested for leaks - none. Touch of condensation here and there, but no leaks.
Plumber said it is completely normal for any condensing boiler system to very gradually lose pressure over time if it has no auto-fill. No way of knowing, but could have been gradually over 2 years in my case.0 -
Scratch, Scratch
If the system is a closed system which this is, where does the water go? Does is evaporate into thin air?There was an error rendering this rich post.
Ugh!
That is bad information. How did he test for leaks?0 -
Reply to JStar "Ugh!"
Here's a quote from the Buderus website:
The pressure loss in a heating system is caused by
air bubbles escaping via fittings and (automatic) air
vents. The oxygen contained in the fresh heating
water will also escape from the heating water after
some time and cause a pressure loss.
Topping up once a year is normal. If it is necessary
to top up more frequently, there might be a leak in
the system or a defective expansion vessel. This
must be remedied as soon as possible.0 -
Pressure
That makes sense...if you have a leak every year.
When you install a boiler, bleed the air, and heat the water, you'll release air from the system one time. After that, how does new water enter the system? It shouldn't, unless there is a leak.0 -
The answer to the question...
Somewhere in your system you have fill valve/prv and a back flow preventer. It usually connects between the expansion tank and air eliminator. There is a lever that will allow you to manually add water to your system. If adding water to your system becomes a regular event, you have a leak that should be addressed. Adding a gallon or so a year is not such a big deal. Some mod/cons, especially Buderus, leak a little. I would not "throw the baby out with the bathwater". Just add some water and keep an eye on it.
Albert Einstein0