Radiator valve bushed down?

Options
I noticed a few of my smaller radiators have their inlet bushed down to what I think is 1" rather than 1 1/4".  Wouldn't this cause the radiator to hold more water rather then allow it all to drain out?



These radiators are around 26-28sqft of EDR.  I'm assuming even if this is technically wrong the fact its been this way for 80+ years means I don't want to mess with it.  But maybe it explains why I have issues with the Hoffman 1As collecting a drop of water in the orifice on these rads.

Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

Comments

  • gerry gill
    gerry gill Posts: 3,084
    Can you post a picture Chris,

    So that we make sure we are on the same page.
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • ChrisJ
    ChrisJ Posts: 17,671
    Radiator picture

    Hi Gerry,



    Here you go, please ignore the 2x12 next to the radiator. I've been using it as a scaffold for painting. Its not a normal bedroom decoration :)

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • ChrisJ
    ChrisJ Posts: 17,671
    edited September 2012
    Radiator picture

    Hi Gerry,



    Here you go. I would think this would cause water to lay in the radiator no matter how much pitch you put on it?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Steamhead
    Steamhead Posts: 18,888
    We see this all the time

    and it works OK as long as the radiator isn't too big. Yours should be fine. 

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

  • gerry gill
    gerry gill Posts: 3,084
    yup, like steamhead says,

    thats a normal install and wouldn't be the problem.
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • All my upstairs radiators are like that.

    They range from 22–36 ft.² EDR.



    On the plus side, if you need to take out the radiator spud, you can usually get the bushing to come out.
    Just another DIYer | King of Prussia, PA
    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
  • ChrisJ
    ChrisJ Posts: 17,671
    Thank you

    all for responding.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Big-Al_2
    Big-Al_2 Posts: 263
    edited September 2012
    Waterfall

    I know the OP is satisfied with the answers already given, but I thought I'd share my experience.



    I have two radiators bushed down like that.  One, a fairly tall one, does make some noise.  It isn't banging or anything like that.  If you listen very carefully while it is filling with steam, it sounds like there is a miniature waterfall inside. Once the vent closes, it gets quiet again. The larger amount of condensate from steam hitting a cold radiator must be trickling into the little pool of water at the bottom. It's a pleasant sound, really . . . unless I need to use the bathroom. 