Radiator valve bushed down?
ChrisJ
Member Posts: 16,316
I noticed a few of my smaller radiators have their inlet bushed down to what I think is 1" rather than 1 1/4". Wouldn't this cause the radiator to hold more water rather then allow it all to drain out?
These radiators are around 26-28sqft of EDR. I'm assuming even if this is technically wrong the fact its been this way for 80+ years means I don't want to mess with it. But maybe it explains why I have issues with the Hoffman 1As collecting a drop of water in the orifice on these rads.
These radiators are around 26-28sqft of EDR. I'm assuming even if this is technically wrong the fact its been this way for 80+ years means I don't want to mess with it. But maybe it explains why I have issues with the Hoffman 1As collecting a drop of water in the orifice on these rads.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0
Comments
-
Can you post a picture Chris,
So that we make sure we are on the same page.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Radiator picture
Hi Gerry,
Here you go, please ignore the 2x12 next to the radiator. I've been using it as a scaffold for painting. Its not a normal bedroom decorationSingle pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Radiator picture
Hi Gerry,
Here you go. I would think this would cause water to lay in the radiator no matter how much pitch you put on it?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
We see this all the time
and it works OK as long as the radiator isn't too big. Yours should be fine.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
yup, like steamhead says,
thats a normal install and wouldn't be the problem.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
All my upstairs radiators are like that.
They range from 22–36 ft.² EDR.
On the plus side, if you need to take out the radiator spud, you can usually get the bushing to come out.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Thank you
all for responding.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Waterfall
I know the OP is satisfied with the answers already given, but I thought I'd share my experience.
I have two radiators bushed down like that. One, a fairly tall one, does make some noise. It isn't banging or anything like that. If you listen very carefully while it is filling with steam, it sounds like there is a miniature waterfall inside. Once the vent closes, it gets quiet again. The larger amount of condensate from steam hitting a cold radiator must be trickling into the little pool of water at the bottom. It's a pleasant sound, really . . . unless I need to use the bathroom.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements