Richardson system
Options
fixitguy
Posts: 100
I have replaced the boiler on a Richardson system, Do I need to have a check valve in the wet return? Also, if I add radiation, do I have to use Richardson valves & traps on the radiators?
0
Comments
-
Don't need a check valve
the Hartford Loop does that job a lot better.
Richardson fittings aren't made anymore. If you can get MEPCO or Barnes & Jones orificing valves, they are the best choice. Use Hoffman 17C traps on the returns, their relatively low air throughput is the closest match for the Richardson ells.0 -
Have a Richardson
We have a Richardson System which had 3 add-on radiators back in the 30's. The add-ons have traditional packless, graduated valves and traps. PIping was altered to remove checkvalve and add Hartford loop. For the most part the system works well, though I would love to convert added rads to Richardson, so if ever you come accross or decide to remove fixtures keep me in mind.
P.S.: Dan had some information in an old Hydronics Magazine article "Dealing with the Richardson System" and I believe he addressed just what you are dealing with. Try contacting him to get info, or it may be in resource section of this site.0 -
ooo
I'd love to read that article. Google has nothing. If anyone knows where it can be found please post it here.0 -
Find what you need?
If you haven't found article, you can google it here on strictly steam site, just google Richardson System, 8 results pop-up, click on 6th title, belief it's PDF etc, then go to pg 12. Good luck!0
This discussion has been closed.
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 132 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 396 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements