Utica DV200A how to wire in Hotwater tank and zone valve for heat
zwulfke
zwulfke Member Posts: 8
Hello
I have a Utica DV200A that i need to wire the Zone for Hot water and the zone for the house. The control box looks as if it does not allow me to do this. Is there a way to wire in both zones to the existing box or will I need to get a control panel?
    Steamhead Member Posts: 18,185
    You'd need to use
    a suitable relay unit which would operate the zones, and call the boiler when a zone was activated. These are available for zoning with circulators or zone valves.
    Consulting
  • Paul48
    Paul48 Member Posts: 4,469
    Zone Valve
    If you're using a zone valve for heat, you'd use another for the hot water.And use a control such as this, for example... http://www.taco-hvac.com/uploads/FileLibrary/100-5.1.pdf