Utica DV200A how to wire in Hotwater tank and zone valve for heat

Options
zwulfke
zwulfke Member Posts: 8
Hello

I have a Utica DV200A that i need to wire the Zone for Hot water and the zone for the house. The control box looks as if it does not allow me to do this. Is there a way to wire in both zones to the existing box or will I need to get a control panel?

Comments

  • Steamhead
    Steamhead Member Posts: 16,842
    Options
    You'd need to use

    a suitable relay unit which would operate the zones, and call the boiler when a zone was activated. These are available for zoning with circulators or zone valves.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Paul48
    Paul48 Member Posts: 4,469
    Options
    Zone Valve

    If you're using a zone valve for heat, you'd use another for the hot water.And use a control such as this, for example... http://www.taco-hvac.com/uploads/FileLibrary/100-5.1.pdf