burnham in4. header?
jonny88
jonny88 Member Posts: 1,139
Hi.I am installing an in4.I am piping 2 two in risers out of boiler.do I have to reduce the equalizer and loop or is it ok to keep everything 2inch.thanks in advance.
  • Danny Scully
    Danny Scully Member Posts: 1,465
    Two things
    Two things, why would you use both tappings? Are you just going the extra mile? If so, good for you! Also, it's certainly ok to keep everything 2 inch, in fact, its preferred (if I'm understanding you right).
  • jonny88
    extra mile
    Im going the extra mile but I just want to make sure I'm not doing it in vain.thanks for your help
    Ø
  • Danny Scully
    Not at all
    Not at all, using both tappings can only help in the production of dry steam. However, you'll want to be carefully how you connect them, but this is all available in the Burnham Literature. As for the Hartford loop, you'll probably want to connect that in whatever size it is now, usually 1-1/4. So you would use an 2 x 2 x 1-1/4 steam tee for example.
  • jonny88
    loop
    The old loop was 1 inch copper ten inches above water line.
  • Danny Scully
    So make it
    So make it a 2 x 2 x 1 steam tee and drop the center line of the Hartford loop to 26 5/8 above the finished floor.