Orifices in mixed system
Options
Fizz
Member Posts: 547
Been reading about use of supply side orifices in rads, wondering if using them in 3 rads added to pre-existing Richardson System would make it more consistent eliminating function of rad traps?
0
Comments
-
If those Richardson valves are original
I believe they already have orificing capability. You might try an orificing valve from MEPCO or Barnes & Jones, this way you can fine-tune it.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
My mistake
Sorry, the added rads are traditional traps, and packless valves circa 1940. The origial Richardson valves are still in place. Would oriface work in added rads?
Fizz0 -
They would work
but would be a bit more difficult to fine-tune. It's much easier to turn a screw.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Orifice closure
Thanks Steamhead.0
This discussion has been closed.
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 49 Biomass
- 424 Carbon Monoxide Awareness
- 72 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 372 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 48 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements