007
007 Member Posts: 2
QUESTIONS ABOUT STEAM BOILERS
WE PLAN TO REMOVE AN OLD KEWANEE STEAM BOILER
AND REPLACE IT WITH A  WEIL McLAIN CAST IRON STEAM BOILER
88 SERIES (WH-BG-788S)  1,358,000 BTU WITH A POWER FLAME BURNER
                                                OR
TYPE (WM-LGB-15)  1,820,000 BTU GRAVITY FIRED BOILER
WHAT IS THE EXPECTED LIFE SPAN OF THESE BOILERS?
WHAT ARE THE ADVANTAGES OR DISADVANTAGES OF THESE TWO BOILERS?
IS A BOILER FEED TANK NECESSARY?
IS  CHEMICAL TREATMENT A GOOD IDEA?
WILL THIS TYPE OF BOILER SHORT CYCLE ON LOW WATER?
WHEN I SET THE NEW BOILER, SHOULD I  SET THE WATER LINE TO THE SAME HEIGHT AS THE OLD BOILERS WATER LINE?
AND IS THIS THE RIGHT THING TO DO?
THANK YOU JIM S.
  • Boiler Talk
    Boiler Talk Member Posts: 144
    007
    Jim,
    Sounds like you need to study this site before you go any further with dumping $10K or more on a system.  Don't quote me on the price I put forth, but it sounds very expensive for the BTU's you provided.  You sound like you don't know what you're writing about.  That's OK.  Nor did I and I feel someone could have told me.  I think that since you started here, we can only guess, you are better prepared.
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,919
    You should read The Lost Art of Steam Heating
    Dan gives several examples of problems that resulted from replacing an old boiler without changing the near-boiler piping. Modern boilers are typically much shorter than the older ones, so their water levels are lower. (You should always run a boiler at its recommended water level.) They also have much smaller steam chests, making near-boiler piping absolutely critical to producing dry steam. You should definitely count on having your near-boiler piping redone, and you should definitely count on having it done by a competent steam technician.
  • Rod
    Rod Posts: 2,067
    Steam Questions
    Hi Jim-
      You ask about the comparison between the two boilers. Since the size of the boiler should be matched to the total EDR, what I'm wondering is why is almost a 500 k BTU difference between your two choices of the boilers.?
    As for your other questions
    IS A BOILER FEED TANK NECESSARY?  - It depends on how slow the condensate return is to the boiler. Ideally one isn't necessary
    IS  CHEMICAL TREATMENT A GOOD IDEA? - Again, the answer it is depends on the water you are using. For more info on this go to the Rhomar Water website.  http://www.rhomarwater.com/products/residential-steam-system/
    WILL THIS TYPE OF BOILER SHORT CYCLE ON LOW WATER? - It shouldn't, if it is setup properly.
    WHEN I SET THE NEW BOILER, SHOULD I  SET THE WATER LINE TO THE SAME HEIGHT AS THE OLD BOILERS WATER LINE?  - Again the answer is - It depends. This is an area where one has to be careful to examine the parameters.
    I would strongly suggest you follow Hap's suggestion and get Dan's book, "The Lost Art of Steam Heating"   http://www.heatinghelp.com/products/Steam-Heating-Books/25/68/Lost-Art-Of-Steam-Heating
    It's easy reading, written for someone new to steam heating, and has the information to answer your questions. Also if you post a question on here we can refer you to a specific page number which has the answer.
    - Rod