007
007
Member Posts: 2
QUESTIONS ABOUT STEAM BOILERS
WE PLAN TO REMOVE AN OLD KEWANEE STEAM BOILER
AND REPLACE IT WITH A WEIL McLAIN CAST IRON STEAM BOILER
88 SERIES (WH-BG-788S) 1,358,000 BTU WITH A POWER FLAME BURNER
OR
TYPE (WM-LGB-15) 1,820,000 BTU GRAVITY FIRED BOILER
WHAT IS THE EXPECTED LIFE SPAN OF THESE BOILERS?
WHAT ARE THE ADVANTAGES OR DISADVANTAGES OF THESE TWO BOILERS?
IS A BOILER FEED TANK NECESSARY?
IS CHEMICAL TREATMENT A GOOD IDEA?
WILL THIS TYPE OF BOILER SHORT CYCLE ON LOW WATER?
WHEN I SET THE NEW BOILER, SHOULD I SET THE WATER LINE TO THE SAME HEIGHT AS THE OLD BOILERS WATER LINE?
AND IS THIS THE RIGHT THING TO DO?
THANK YOU JIM S.
WE PLAN TO REMOVE AN OLD KEWANEE STEAM BOILER
AND REPLACE IT WITH A WEIL McLAIN CAST IRON STEAM BOILER
88 SERIES (WH-BG-788S) 1,358,000 BTU WITH A POWER FLAME BURNER
OR
TYPE (WM-LGB-15) 1,820,000 BTU GRAVITY FIRED BOILER
WHAT IS THE EXPECTED LIFE SPAN OF THESE BOILERS?
WHAT ARE THE ADVANTAGES OR DISADVANTAGES OF THESE TWO BOILERS?
IS A BOILER FEED TANK NECESSARY?
IS CHEMICAL TREATMENT A GOOD IDEA?
WILL THIS TYPE OF BOILER SHORT CYCLE ON LOW WATER?
WHEN I SET THE NEW BOILER, SHOULD I SET THE WATER LINE TO THE SAME HEIGHT AS THE OLD BOILERS WATER LINE?
AND IS THIS THE RIGHT THING TO DO?
THANK YOU JIM S.
0
Comments
-
007
Jim,
Sounds like you need to study this site before you go any further with dumping $10K or more on a system. Don't quote me on the price I put forth, but it sounds very expensive for the BTU's you provided. You sound like you don't know what you're writing about. That's OK. Nor did I and I feel someone could have told me. I think that since you started here, we can only guess, you are better prepared.0 -
You should read The Lost Art of Steam Heating
Dan gives several examples of problems that resulted from replacing an old boiler without changing the near-boiler piping. Modern boilers are typically much shorter than the older ones, so their water levels are lower. (You should always run a boiler at its recommended water level.) They also have much smaller steam chests, making near-boiler piping absolutely critical to producing dry steam. You should definitely count on having your near-boiler piping redone, and you should definitely count on having it done by a competent steam technician.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Steam Questions
Hi Jim-
You ask about the comparison between the two boilers. Since the size of the boiler should be matched to the total EDR, what I'm wondering is why is almost a 500 k BTU difference between your two choices of the boilers.?
As for your other questions
IS A BOILER FEED TANK NECESSARY? - It depends on how slow the condensate return is to the boiler. Ideally one isn't necessary
IS CHEMICAL TREATMENT A GOOD IDEA? - Again, the answer it is depends on the water you are using. For more info on this go to the Rhomar Water website. http://www.rhomarwater.com/products/residential-steam-system/
WILL THIS TYPE OF BOILER SHORT CYCLE ON LOW WATER? - It shouldn't, if it is setup properly.
WHEN I SET THE NEW BOILER, SHOULD I SET THE WATER LINE TO THE SAME HEIGHT AS THE OLD BOILERS WATER LINE? - Again the answer is - It depends. This is an area where one has to be careful to examine the parameters.
I would strongly suggest you follow Hap's suggestion and get Dan's book, "The Lost Art of Steam Heating" http://www.heatinghelp.com/products/Steam-Heating-Books/25/68/Lost-Art-Of-Steam-Heating
It's easy reading, written for someone new to steam heating, and has the information to answer your questions. Also if you post a question on here we can refer you to a specific page number which has the answer.
- Rod0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements