Compressor shut down
Jim Pompetti
Member Posts: 552
I have a unit thats shutting down , on high anbient conditions . Runs well , when we get to 100 ° F it trip the breaker.
Breaker
What is "circuit breaker ampacity "of the unit and what breaker is in the panel and what amps is the unit pulling?0 -
Need some info
Pressures and temps at 100* if possible. Condition of contactor and electrical in general. Amp draw on compressor and cond. fan. All you are saying is it's broke at 100*, please fill in the blanks.
Mike T.0 -
Need more info.....
As Empire said, need more info. Could be so many things. Amp draws and superheat/subcooling. Also capacitor weak? Outdoor fan motor going out on internal overload? Does the unit have a high pressure switch? Electrical connections tight? Proper wire size? May need hard start kit.0