Is it possible to Introduce a 2-Pipe Radiator into a 1-Pipe System?
SewardWasRight
Member Posts: 12
The system is an original 1-pipe.
All of my radiators are 1-pipe.
The radiator in question (a "Bundy Columbia"?) has the two (supply and return?) trappings on one side at the bottom, and a space for a vent on the other end about 1/3 of the way down from the top of the radiator.
It is a nice radiator, but not sure if it is worth what is needed to change any piping or do any conversions to the radiator itself.
I am new to steam and so I thank you all in advance for your help,
Brian
Brian
In a word -yes,
however you are in for some piping work in order to accomplish it.gwgillplumbingandheating.com
Piping - as in changing the current valve or hooking 2-pipe pipes up to it?
Would this involve anything other than a set of pipes coming out of the radiator and joining at a common spot before going into the currently insstalled valve? Is there any documentation on this that I could follow?
Also, can the radiator be converted to one pipe by closing one of the trappings and piping the radiator with one pipe?
Thanks again,
Brian0 -
No, it wouldn't be that easy,
the outlet (return) would need to duck down under the floor most likely and then come back up in order to make a water seal..and then tie into the piping. I dont think you could plug one side and pipe it one pipe unless the tappings are large..what size are they?gwgillplumbingandheating.com
The larger of the two trappings is approx. 1 3/4" at the opening of the pipe.
It appears to be about the size of a regular 1-pipe opening.
The other side (the return?) is smaller.
B0 -
You
might find this interesting... http://archive.org/stream/bundyradiatorsfo00aagrrich#page/26/mode/2up0 -
Paul48- thats a treasure of a find!
Thats one heck of a great find! Well done..looking thru that it would appear that potentially he could hook that radiator up..maybe someone can weld together a copy of that triple tapped inlet fitting..perhaps out of pipe or square tubing..again, thanks for the great find on the catalog!gwgillplumbingandheating.com
gerry
I wanted to get a look at the Bundy Columbia, that's all, but found that beauty. How about some of those works of art! Evidently, Mr. Bundy invented the Bundy Loop. I may be wrong, but I believe it is the section of a cast iron radiator that we are all familiar with. It was said to have revolutionized heating. Did you see the duplex radiator? Or, the boiler controls?0
