Heat Load for greenhouses.
Options
Wayco Wayne_2
Member Posts: 2,479
How do you do a heat load for a greenhouse? there's no walls, only glass. A little help please.
0
Comments
-
R what?
Single pane would be R 1 to 2, double pane could be R 3 to 5 (with gas) and triple pane could be R 5 to R 7 (also with gas).
Infiltration could be the killer..
A over R times delta T = conductive losses.
Plus infiltration at .018 btu/cu ft/minute times the air changes per hour.
ME0 -
Greenhouses are a little different.
While Mark's method is the more scientific approach, the greenhouse people usually have a heating package geared for the horticultural intent.
They are usually done for Seasonal, Local, Tropical, etc... That drives the design temp and humidity. Tropical greenhouses are normally designed for 84 F year around indoor temp. Seasonals are 72 F shoulder and 60 F winter indoor temp.
Greenhouses are the only buildings that I do a radiation only survey on for boiler replacements and even new installations. Because the greenhouse folks always spec the radiation amounts.
Good Luck.0 -
Thanks
for the input. There are two old rusty peerless boilers rated at 845,000 IBR. There is a primary loop out to the greenhouses with pairs of close tees and a circulator every place they want a zone. I'm thinking of taking out one boiler and putting 2 or 3 mod cons in its place. (for economic reasons.) I'd have all boilers teed into the primary loop and a boiler control staging the boilers in and out. I'd use the old peerless cast iron beatie as the last dollop of heat in the colder weather. I will do a heat load but I agree it would only be a SWAG0 -
Delivering Heat
What are you using to deliver heat in the greenhouse?
Thanks, Bob GagnonTo learn more about this professional, click here to visit their ad in Find A Contractor.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements